Discuss Sunhouse Sshe125 fan not working in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello and good evening

I have been asked to take a look at a Sunhouse sshe125 storage heater.

The heater’s fan is not working and Dimplex have suggested the fan needs replacing.

This afternoon I bench tested the fan motor and it operates, so I am now scratching my head.

The unit heats up but the fan doesn’t operate. I have checked all connections and they are all in order.

I have reset the unit but no luck.

The client said that they occasionally get an 02 error code but this is not there anymore.

Can anyone suggest what the issue might be?
 
Can anyone suggest what the issue might be?
Not familiar with these but the cct shows there are two thermostats in series with the fan at the bottom - presumably to turn it off when the room is hot!
A continuity check from the controller fan connections to the fan itself might be worthwhile?
Are you able to get to the pcb to check if there is mains out to the fan when it's supposed to be running?

Presumably the on-peak supply is there as well as off-peak, and the controller is showing signs of life!

47E187B9-ABC8-476E-99FD-4F2015009E97.jpeg
 
Not familiar with these but the cct shows there are two thermostats in series with the fan at the bottom - presumably to turn it off when the room is hot!
A continuity check from the controller fan connections to the fan itself might be worthwhile?
Are you able to get to the pcb to check if there is mains out to the fan when it's supposed to be running?

Presumably the on-peak supply is there as well as off-peak, and the controller is showing signs of life!

View attachment 104585
Thank you Avo Mk8

I was actually looking at the wiring diagram last night.

I will check today the voltage coming to the motor/fan, I am assuming nothing as the motor would operate.

I will also check the voltage from the PCB where the motor connects, I am guessing if there is voltage there that the suspect part will be the "stats", I am guessing if there is no voltage from the PCB then it is the controller that has malfunctioned.

The unit has both Peak & Off Peak supply and the temperature of the bricks is very work, so I know the controller is requesting demand to heat the bricks.

Thanks,

Rob
 

Reply to Sunhouse Sshe125 fan not working in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have an Economy 7 storage heater Dimplex CXL24N - 3.4kW Storage Heater + Convector ( there not available anymore) that dos'nt work and...
Replies
0
Views
540
I'm sorry if this isn't in the right place but this is my first time using this forum. I'm also sorry if i make some mistakes but I'm new to this...
Replies
6
Views
1K
Has anyone taken apart their & self repaired it? 2013 Dodge Grand Caravan SXT - Mileage: 112223 - DTCs - P0480 cooling fan. Also codes in TIPM...
Replies
0
Views
664
I have a ceiling fan which currently has a remote control for fan speed and dimming the attached lights. We're currently doing some works in the...
Replies
6
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
164

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock