Discuss supply to outbuilding in the Electrical Forum Canada area at ElectriciansForums.net

Reaction score
69
can some one please correct me according to 17th you can no longer protect all your circuits by one rcd and you have to spilt your circuits with 2 rcds so down stairs lighting on one and upstairs lighting on the other or individal rcbos for each circuit.question is if i supply a second ccu in a out building and it has 2 ways protected by a rcd will this pass 17th as the rcd will knock lights out and sockets at same time
 
can some one please correct me according to 17th you can no longer protect all your circuits by one rcd and you have to spilt your circuits with 2 rcds so down stairs lighting on one and upstairs lighting on the other or individal rcbos for each circuit.question is if i supply a second ccu in a out building and it has 2 ways protected by a rcd will this pass 17th as the rcd will knock lights out and sockets at same time

quite specifically Reg 314.1

your sub-cu will be fine, presuming socket outlets and lights is all thats on there?

and you couldnt protect them all on one RCD in the 16th, nothing much has changed, just the additional RCD requirements have 'highlghted' something that has always been there;)
 
THE 17TH EDITION BOARDS CAN BE VARIOUS CONFIGURATIONS
The dual rcd seems to be the type thats taking favour with most people
In the 16th one rcd covering the whole of the installation was a deviation because it did not allow discrimination between say the lights and sockets
The 17th regulations require rcd additional protection for mostly everything in a domestic dwelling unles its surface wired,so the double rcd is being touted with up lights on rcd with down sockets etc and other configurations as well
It seems to me that the single rcd covering the whole of the installation was never no major problem(In fact I have this in my own home and its never been a nuisance as far as tripping everything off causing mayhem is concerned)
The 17th requirement will be a problem when adding lights and such to existing installations
How many people will use a double rcd for discrimination then (not many I would think)
So why the option of one rcd is frowned on by many is not a big problem in my estimation
Additions will be provided with one rcd where necessary and no thought given to discrimination in these cases ,so why do we be so concerned for new installs
Bring back the one rcd over the whole of the installation if thats whats wanted I say
and forget this dual rcd game of picking which team the up lights are on
Things are being over complicated with little advantage being gained


I take so long to type these essays out I get logged out
Getting more and more annoyed with this function lately
 
THE 17TH EDITION BOARDS CAN BE VARIOUS CONFIGURATIONS
The dual rcd seems to be the type thats taking favour with most people
In the 16th one rcd covering the whole of the installation was a deviation because it did not allow discrimination between say the lights and sockets
The 17th regulations require rcd additional protection for mostly everything in a domestic dwelling unles its surface wired,so the double rcd is being touted with up lights on rcd with down sockets etc and other configurations as well
It seems to me that the single rcd covering the whole of the installation was never no major problem(In fact I have this in my own home and its never been a nuisance as far as tripping everything off causing mayhem is concerned)
The 17th requirement will be a problem when adding lights and such to existing installations
How many people will use a double rcd for discrimination then (not many I would think)
So why the option of one rcd is frowned on by many is not a big problem in my estimation
Additions will be provided with one rcd where necessary and no thought given to discrimination in these cases ,so why do we be so concerned for new installs
Bring back the one rcd over the whole of the installation if thats whats wanted I say
and forget this dual rcd game of picking which team the up lights are on
Things are being over complicated with little advantage being gained


I take so long to type these essays out I get logged out
Getting more and more annoyed with this function lately

but what about the smokes Des?

Ideally they should not be on an RCD, but if the supply cable for them is buried, then they may have to be

so then they cant be on the same RCD as sockets

difficult to achieve with one RCD? Of course we could go RCBO, but that is to comply, and if we are goiung to comply the 314.1 applies
 

Reply to supply to outbuilding in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
946
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
823

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock