uksel

just having a scan through the examiners notes posted regarding the 2391

noticed on of the comments made was

'
"could not state the minimum test voltage to be used and the minimum acceptable value of insulation resistance when carrying out a insulation resistance test on a circuit containing surge protected socket-outlets"


I cant find specific reference to this anywhere, are they looking for test 2, IR to earth with Line & Neutral connected together??

or would they be asking for a soft test at 250v.


really looking for a page or regulation reference for confirmation if anybody has any insight?

 
Yes,I think they are making critisism of perhaps poor overall satisfactory answers to the problem set rather than a specific regs reference
It would be test 2 at 500v where the items could not be dis connected
Gn3 page 38 would probably be the nearest
 
well funnily enough, i'm having a look at the february exam paper (from which this examiner feedback was apparently given)

Q15. An insulation resistance test is to be carried out on a radial circuit supplying socket outlets that incorporate surge protective devices (SPD's). State the TWO procedures identified in BS7671 that permit the test to be carried out



now, that is the exact working of the question, so there are two main things to highlight here

1. there are aparrently two procedures for this specific example given
2. it specifically relates to references in BS7671 that 'permit' the tests to be carried out


i'm searching but not coming up with anything, yet in the eyes of C&G and the examiner, this is information that every candidate should know (it is also specifically highlighted in their own exam success book).
 
Last edited by a moderator:
From 612.3.2 I would say the two procedures are:

1) Test with the SPDs disconnected or, where it is not reasonably practicable to disconnect
2) Test at 250v dc, but still adhere to a minimum reading of 1Mohm
 
good find julianc :)

having read that, i would 100% agree with

1. disconnect before carrying out the test
2. reduce test voltage to 250v but with a resistance value of at least 1 ohm


though it begs the question, would SPD's & similar have a resistance of greater than 1 Megaohm?
 

Reply to Surge Protected Socket Outlets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
989
I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
Scratching my head a bit on a job today. Been to clients house to investigate fault with installation. For the past few months client has...
Replies
10
Views
6K
My customer read on many forums about people suffering to solve a problem with the above Land Rover with regards to a fault code known as P1260...
Replies
5
Views
29K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock