Discuss Surge Protection Device on old installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

punkin

-
Reaction score
14
Hi
I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back.

Our company just had its EICR done. The tester gave us a C2 for a number of DB’s which don’t have Surge Protection Device installed, these DBs with the C2 do have lighting and emergency lighting circuits.
Do we have to have these SPD’s installed now because of 18th edition amendment 2 or should it be a C3 for a recommended device in the DB’s for old boards.

Many thanks.
 
C1 – There is a danger present, risk of injury and immediate remedial action required.
C2 – There is a potential danger present and urgent remedial work is required.
C3 – Improvement is recommended.

how can anyone justify a surge protection issue as a potential danger?
 
C1 – There is a danger present, risk of injury and immediate remedial action required.
C2 – There is a potential danger present and urgent remedial work is required.
C3 – Improvement is recommended.

how can anyone justify a surge protection issue as a potential danger?

Perhaps they identify as a delicate piece of electronic equipment.
 
I presume that the reasoning is that there are life safety systems present (i.e. the emergency lighting installations). That said I would probably personally consider the classification of the Observation to be rather harsh.
 
C1 – There is a danger present, risk of injury and immediate remedial action required.
C2 – There is a potential danger present and urgent remedial work is required.
C3 – Improvement is recommended.

how can anyone justify a surge protection issue as a potential danger?
Exactly, having no SPD isn't a potential danger with urgent remedial work required.
 
I presume that the reasoning is that there are life safety systems present (i.e. the emergency lighting installations). That said I would probably personally consider the classification of the Observation to be rather harsh.
I agree, its defiantly harsh to put it as a C3
 

Reply to Surge Protection Device on old installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
510
Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello! I'm struggling to find an answer to this question online. I'm new here btw - I'm a DIYer with a physics degree Currently when my fridge...
Replies
19
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock