Discuss SWA joint the steel of a 2 core in the UK Electrical Forum area at ElectriciansForums.net

Joint it to the dB or joint cable to Cable
 
If you have to join cables mid-way then something like this has all the bits you need and is properly waterproof if you follow the instructions precisely:
https://www.cef.co.uk/catalogue/pro...-resin-joint-kit-for-cables-up-to-16mm-2-core

But usually you use the glands at the ends and avoid joints if at all possible.
Thank you. The client wants to use this SWA(it is for temporary use)most likely to save money. However I have missed the green insulated conductor included in the kit which will give the continuity of the steel. Glands will be provided on both side.
 
More importantly, is the armour suitable for using as a cpc for your circuit design?
 
Thank you. The client wants to use this SWA(it is for temporary use)most likely to save money. However I have missed the green insulated conductor included in the kit which will give the continuity of the steel. Glands will be provided on both side.
So the jointing kit is missing the earth link?

10mm 2-core has armour equivalent of 26mm steel = 3.25mm copper approx (6 ohm / km) so you would need some copper braid of roughly 4mm CSA as a replacement. Depending on the space available it might be a case of using 2 * 2.5mm stranded insulated wires, but you would need to be very sure it was making a proper connection when clamped.
 
More importantly, is the armour suitable for using as a cpc for your circuit design?
First thought that went through my head, too!
 
I am reading the original post as "how do I connect the armour of the SWA to consumer unit, and also to the DB".

Answer - use the proper type and size of gland for the SWA cable, along with the supplied earth connection ring (banjo) bolted through the metalwork using brass bolts and nuts.

Or is it just me?
 
Like PC1966 just said OP mentioned link missing so assumed it to involve a joint kit!! but could be wrong, its not very clear!
 
I read the OP as
I have a 2 core 10mm2 SWA from a DB to a consumer unit to be joint.
and with a little imaginative spelling correction i get:

"I have a 2 core 10mm2 SWA from a DB to a Consumer unit to be JOINED"

So I think the suggestion of the torpedo joints with resin is right. Also the copper equivalent of the missing earthing link between the two armours.
 

Reply to SWA joint the steel of a 2 core in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
718
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
744
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
973
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
708
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock