- Reaction score
- 2,392
Doing calcs on swa supply to building as sub main from main three phase squard D board for single phase supply off of TN-S supply. I used cable mate from jarsoft and looked up various tables for disconnection times. In all case scenarios it tells me it will not disconnect within the required time. The Ipf at .211K is insufficient fault level. This is based on calculating EFLI on 16mm² being 1.091 and the max Zs Ohms being (table 41.3) 0.69. Vd has been calc. and is ok. This also assumes 5s disconnection time based on being a distribution circuit. It is also based on using type B 61009. Which is what is throwing me as at 1667 ohms it should be absolutely fine. Am I missing something here or is the Cable Mate software wrong?
See calc sheet included.
See calc sheet included.