Hi,
I am installing 12 x suspended LED fittings in an office. They are on two switches. The fitting itself comes with a 5 core cable. How do I switch this. Do I need on/off and momentary switch or something else. See attached pic. Any ideas gratefully accepted.

043F6F8E-6FA0-4288-883E-41C405157142.jpeg
 
as above.you will need a 5 core cable to the switch, which will be on/off with a variable 0V -10V output.
 
Thanks for quick replies.I thought as much , I wired the lights with 3 core cable plus a cat 6 for the dimming control. My problem is that the switches for the lights are on a grid. In the past when I’ve dimmed fluorescents before I’ve had a permanent feed and neutral to fittings and a momentary switch for the dimming control. This doesn’t appear to work on my dimmable LEDS . Does each switched run need two switches, an on off then a separate 1-10v dimmer. I have a 4 gang grid switch and was hoping to just use up two places.
 
Thanks again for all your help ive found what i need. Its a varilight

Product Description: 2-Way Dimmer for Multiple HF Ballasts/LED Drivers requiring 1-10V DC Input (To fit MK, Schneider Ultimate, Schneider Lisse, Crabtree, Hager, Deta, BG & Varilight PowerGrid)
 

Reply to Switching of suspended dimmable led fittings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

R
I am looking into LED lighting for a Grade I listed church, parts of which are 800 years old. The lighting must be simply dimmable with a colour...
Replies
3
Views
380
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
668
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
635
The following light fitting from Dumelm takes GU10 but states "Dimmable No" but I can't see why with the correct dimmer switch and dimmable GU10...
Replies
2
Views
676
Hi all, I am trying to replace my halogen wall uplights (230W, 240V, R7S, 114mm) with LED but so far no luck. I've tried both of the below LEDs...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock