As @westward10 pointed out your usual RCD test would not reliably test-trip a VOELCB but if it dumps enough current in to the CPC system to get raise that to the required potential above the Earth rod then it will trip.

Is the system TT at it appears from the picture of the cut-out? Typically that was the use-case for them but not a very good or reliable system compared to RCD style protection.

Probably best to have RCBO boards, but they could be replaced by 2 * 100mA delay RCDs if those boards and the old time-switch are being kept. You could use a 4P to do the same job the same way, but it is a bit of a mess, with red tail cable used for one of the neutrals as well!
Okay gotcha.
Yes it's a TT system, but a good reading, was around 6.5ohms iirc, though it's a very old installation as you can see, so the rod has well and truly bedded in.
There isn't an option to carry out any further work at present as the chap is elderly, and dare I say, lives in squalor. It was a very grim visit and felt the need to run home to shower afterwards.
Nice chap though, just very old school and set in his ways I think.
I replaced the ELCB with an RCD, then actually found further issues including a faulty kitchen ring circuit.
The whole house was an accident waiting to happen.
He'd had a water leak from the bathroom pipes, soaked the downstairs ceiling causing the lights on the ground floor to fail, and the previous electrician just left it to dry out but still powered up and not working...
That was 2 years ago, lights still don't work, I suspect a break somewhere.
I digress, I really hope to never get a call back there.
 
If it is TT the earths appear to be in the same terminal if so this is incorrect. The electrode should go into E and the installation earth into the other one, probably F.
 

Reply to Take a close look where the tails are routed! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
619
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
378
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock