Hi,

Initially not sure of where to put this post as it touches more that one forum.

Grateful for your help please with an unusual installation.

I am looking to avoid long runs of hot water from the combi to the launderette due to being on a water meter and to run the taps until hot water is ejected is wasteful.

I am thinking of tankless undersink instant water heaters that heat up the cold supply at the tap but at 3kw can be spurred into the ring main. However, they only achieve about 1.2 litres per minute for a 30C temperature rise.

Grateful for your views/considerations on wiring up two such heaters in parallel to achieve either 2.4 liters per minute or a 60C rise at 1.2 litres per minute. This would pull 6KW of the ring main approaching shower teritory. However is the same as running say three 2KW fan heaters in different rooms off the same ring? The heater manufacture is OK with feeding one heater into the other but I am unsure of the electrical supply issue.
 
Water heaters of volume greater than 15litres are supposed to have their own dedicated electrical supply.
A ring final circuit is not designed to support loads of that magnitude.

You would be better off having a single small hot water tank with an immersion heater in it to act as a hot water buffer. Not sure how that would work, plumbing-wise.
Even so, the immersion should really have its own separate supply.
 
As above but won't two in parallel achieve the same temperature but just double the volume.
 
Thanks all for your comments.

Hi Ruston - It's a domestic situation.

Hello Westward - Yes either the volume would double (which is my ideal aim) or the temperature rise would increase depending upon how much you turn the tap on. Typically the heaters are limited to 50C but in practise rarely achieve this due to the poor draw volume. At the recommended 1.2 litres per minute would take a noticeable time to fill up a bowl of water to wash something by hand in the sink. A doubled up volume would be useful at 30C rise.

I thought about the small water tank option but they would maintain 5 -10 litres of hot water that is not used often and would not be 'green'. I liked the idea of only heating what you need with the new instant heaters.

Andy - that's a fair point, only 8 amps left on the ring.
 
That is along the lines I was thinking.
If cost is the only consideration heating with electricity will cost more than the wasted cold water ,But you will also be wasting the hot water left in the long run pipe.
I would be looking at getting the source of the heating nearer the demand if it is high.
Electricity would be my last choice if it is.
 

Reply to Tankless instant water heaters in parallel in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hello, I am looking at getting a solar PV installation (8 x 350W plus 4.6 kWh battery) and wondered how I might best take advantage of it when...
Replies
1
Views
3K
Dear community, as the Pro Nest are too fare away from my place in Italy, I am seeking here for advice. The actual work will be done then by my...
Replies
1
Views
1K
Hello all, I will try and make this a painless as possible but grateful for anyones thoughts. I am currently contracted to install heaters for...
Replies
2
Views
11K
D
Hi everyone I try to buy/find a Instant tankless electric water heater in uk as the flat I living in have no gas and I want instant hot water...
Replies
32
Views
14K
DuckyUC
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock