Can anybody help with this one?

Installation: TT system, (Ra 27 ohms), 3 phase & neutral incoming supply.

A 4 pole 30mA RCD is at the head of the board, from which there is a 3 phase motor circuit and a 3 phase & neutral feed to a second board. The second board has a number of 230V final circuits fed from each of the phases in turn.

When testing the RCD I get a figure of about 120mS at 30mA test current but at 150mA test current the test bombs out at >40mA. I can't actually configure the test set to record the operating time at 5 x Idn.

I changed the RCD for a new one and I get the same result.

I started off by testing this at one of the 230V final circuits. However, I get the same result if I test directly on the output terminals of the RCD - i.e. L1, N, CPC - ditto L2, L3.

I have checked the tester on a 2 pole 30mA RCD and I get the normal sort of operating times you would associate with a fully functioning device.

Any thoughts on the test method, or a configuration fault which might give longer than expected cut-off times?
 
Can anybody help with this one?

Installation: TT system, (Ra 27 ohms), 3 phase & neutral incoming supply.

A 4 pole 30mA RCD is at the head of the board, from which there is a 3 phase motor circuit and a 3 phase & neutral feed to a second board. The second board has a number of 230V final circuits fed from each of the phases in turn.

When testing the RCD I get a figure of about 120mS at 30mA test current but at 150mA test current the test bombs out at >40mA. I can't actually configure the test set to record the operating time at 5 x Idn.

I changed the RCD for a new one and I get the same result.

I started off by testing this at one of the 230V final circuits. However, I get the same result if I test directly on the output terminals of the RCD - i.e. L1, N, CPC - ditto L2, L3.

I have checked the tester on a 2 pole 30mA RCD and I get the normal sort of operating times you would associate with a fully functioning device.

Any thoughts on the test method, or a configuration fault which might give longer than expected cut-off times?


The above,may possibly be a clue,to what Lee has already mentioned :rolleyes2:
 

Reply to testing 4 pole RCD - funny results? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
833
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock