Currently reading:
Testing exam question

Discuss Testing exam question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
26
Hi I’m looking to confirm something quickly, I’m due to sit a practical exam next week run by napit , this is to prove competence as haven’t got a testing and inspection exam .

I understand the test procedures and looking at course content etc I have to carry out the following

1. electrical installation condition report
2. Initial verification
3. Minor works

now my question is when carrying out an initial verification when should you test the

Ze , pfc ??? Now under gn3 this states to carry Out in this order - conti of cpc, including main and supplementary
Conti of ring circuits
InsuLation testing
Polarity

then carry out earth fault loop impedance, is this where I would do my Ze and Zs tests???
Then pfc test????

used to looking at condition reports so generally do my ze test once locked of main switch - but don’t want to fail exam on initial verification so need to make sure I test the ze at right time. Just seems to be a long way into testing before ze is taken .
 
The trainers are to make sure you pass looks bad on them if they get a lot of failures
Thats not the case here Pete, they're not trainers they are invigilators.

They are there to observe the tests are performed under exam conditions.

I don't believe there is a course associated with this certificate it is purely, supposed to be, an assessment of competence.

I was explicitly advised that this was not a training course but an assessment and that coaching would not happen.

So I believe its more a case of collecting subs of new scheme entrants.
 
Alright mate,

I take it you’re doing the Napit 7232 to prove competence? If so, read below.

You’ll be given a bay containing a 3P and single phase boards containing various circuits, containment, bonding, sup bonding and wiring types, to simulate something along the lines of a commercial premises downstairs and a residential dwelling above it.

First up you’ll have half an hour to carry out a visual inspection and pick up as many faults as possible, there’s about 12 and they like you to get at least 10. The rest you’ll pick up while testing.

Then you’ll do an EICR on the 3P board in the morning and an EIC on the SP board in the afternoon. You’ll also do a MWC for a spur that’s been put in on the RFC on the SP board.

At this point I’ll note that the 3P board is supplying the SP board.

Go through the testing sequence as you would.

Safe isolation
Continuity of main earthing conductors
Continuity of Bonding and sup bonding
Continuity of circuit protective conductors and RFC’s
IR
Live polarity at incoming tails
Ze
PEFC
PFC
Phase Rotation

Check over the board, make sure you’ve left nothing hanging out, replace guards and board cover.
You can now carry out Zs of circuits, RCD tests and functional tests.

IMPORTANT - Ensure the cover is on your 3P board and your SP board locked off before you take a Zs reading there, as although they’re right next to each other, in reality, ones in a basement and ones up the stairs. You’ll also need to prove safe isolation on the SP board prior to taking the reading.

Time wise, I think you get 2 hours for the EICR and 2.5 hours for the EIC and MWC which is plenty as on a 2391 course you only get 2.5 hours to complete both.

Good luck with but all; and if I’ve put phase rotation in the wrong place, I’m sure someone will be here to correct me shortly.

One more thing - SAFE ISOLATION, SAFE ISOLATION, SAFE ISOLATION
Very good of you to give this information, I also have the 7232 practical, do you know if the CU has rbco circuit or mcb
 
Very good of you to give this information, I also have the 7232 practical, do you know if the CU has rbco circuit or mcb

From memory, there was no RCD on the 3P board, and SP board was split load duel RCD for additional protection.

However, it’s been a few years so they may have updated the rigs (doubtful), and I suppose each training centre could be a different set up, so may not be the same.

You’ve got a rough idea of what to expect though.
 
From memory, there was no RCD on the 3P board, and SP board was split load duel RCD for additional protection.

However, it’s been a few years so they may have updated the rigs (doubtful), and I suppose each training centre could be a different set up, so may not be the same.

You’ve got a rough idea of what to expect though.
Yes got a good idea, just want to make sure I think about every possible scenario. Many thanks for you help it is very much appreciated.
 

Reply to Testing exam question in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock