Completed a new install recently. 45a 10mm2 SWA Sub main (TT) to an outbuilding and 2 x final circuits- 32a Ring and 6a lighting, nice and simple. Customer might require additional circuits in the future, hence the 10mm2 SWA.

Tested the Ring Circuit- end to end all good and as expected. Then r1+rn/4 & r1+r2/4 results all over the place!! Removed all socket fronts x8 and tested at the terminals, perfect readings! So concluded that the pin contacts are unreliable and giving high resistances. They are axiom DP 13a 2 gang socket outlets. Has anyone else had problems similar with these?? Not experienced it before but not sure if contact spray will do the job either!?
 
It might be worth double checking your plug-in tester lead too.

I don't normally buy Axiom sockets (Toolstation?) after getting 2 in an order that simply didn't work, but that was a long while ago to be fair.
 
It might be worth double checking your plug-in tester lead too.

I don't normally buy Axiom sockets (Toolstation?) after getting 2 in an order that simply didn't work, but that was a long while ago to be fair.
Hi, yes test leads/plug all in working order. They are metalclad sockets from toolstation- the customer chose them and although I haven’t used axiom before, they didn’t seem too bad quality when 2nd fixing.
 
Hi, yes test leads/plug all in working order. They are metalclad sockets from toolstation- the customer chose them and although I haven’t used axiom before, they didn’t seem too bad quality when 2nd fixing.
Cos they were cheap and they didn't realise how low quality Axiom are

IMO using Axiom once is too often and buying them is a mistake never repeated
 
As a hunch I would say it's more likely to be the switch contacts rather than the actual socket, however we've seen particular types of socket that had abnormally high resistance at the socket itself. High resistance contacts fall into two main groups; those due to tarnish that give high readings on a continuity test but work fine when the film is broken down by the application of mains, and those due to faulty construction / lack of pressure that are properly high-resistance and will overheat under normal load. If you want to cheat, try energising it and switching a kettle on and off a couple of times before retesting. You shouldn't have to do that with new sockets though!
 

Reply to Testing issues!! Dodgy 13 A socket contacts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
273
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock