Discuss Testing station and making it safer? in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hi guys,

We have a little test station at work for checking the operation of electrical safety brakes, clutches and electromagnetic coils. The 230 AC all feed into different rectifiers... 24vdc...104vdc.. 207vdc...

It runs off a plug top, max current is about 6A but I'm wanting to make a bit of a more organised arrangement and add some more protection. Could I use a MCB/RCD before all these rectifiers? Maybe some sort of inline fuse?

Thanks.
 
Hi guys,

We have a little test station at work for checking the operation of electrical safety brakes, clutches and electromagnetic coils. The 230 AC all feed into different rectifiers... 24vdc...104vdc.. 207vdc...

It runs off a plug top, max current is about 6A but I'm wanting to make a bit of a more organised arrangement and add some more protection. Could I use a MCB/RCD before all these rectifiers? Maybe some sort of inline fuse?

Thanks.


Why a MCB? What is wrong with the plug fuse?
If the circuit is not RCD protected you could fit something like this.

or changed the socket to one with a RCD...
 
Last time I was involved in a bench test set up, we used 10mA RCDs.
 
No reason dude. Just wanted it to trip first for resetting purposes.

I'm presuming this reply is for my "Why a MCB? What is wrong with the plug fuse?" question.
The plug fuse should always blow before the circuit MCB trips.
 
I'm presuming this reply is for my "Why a MCB? What is wrong with the plug fuse?" question.
The plug fuse should always blow before the circuit MCB trips.

It is yes. Thank you. Just wanted to check that the plug fuse is an acceptable primary failsafe. Often the equipment can have faults that we test.
 
It is yes. Thank you. Just wanted to check that the plug fuse is an acceptable primary failsafe. Often the equipment can have faults that we test.

What type of faults mate? Things that RCD will solve or things that blow the fuse?
I wouldn't want to keep replacing the fuse in the plug all the time. I would fit a box with a reset fuse. (pop-up fuse... or whatever they are called)
 
It's rare, but sometimes the rectifiers can be faulty and also the coils. We test them for continuity but sometimes they are partially shorted and pop the fuse. It's not often at all. Just wanted it to look neater and more professional really.
 
Why not test for faults before energising things?

I would agree that this should alway be step one of any test. You could add some kind of ohmmeter to the bench and a list of resistance measurements for each type of device to be tested.
 
It's rare, but sometimes the rectifiers can be faulty and also the coils. We test them for continuity but sometimes they are partially shorted and pop the fuse. It's not often at all. Just wanted it to look neater and more professional really.

If you test continuity why don’t you test for faults at the same time?
 
I always test them for faults. Both the resistance of the coil and to ground before i switch on. The other guys sometimes don't however..
 
If there are anymore tests I should be doing. Please do let me know. I purposely posted this on the DIY section to allow for any uncertainty in what I'm saying. I test all the diodes with the continuity setting then energise all bridge and half wave rectifiers - then test the voltage drop across each diode... i then check the output is a smooth DC with the scope and the coils for the manufacturers ohm +/- 10%..

I also probe the body of the safety brake and put it to earth and see if I have any obvious faults with low resistance.

We have just been wanting to make this little rig the right way, both to look, act and behave safely. Im primarily from an electronics background so I'm under no illusion my electrical industry skills are a bit s**t.
 
I always test them for faults. Both the resistance of the coil and to ground before i switch on. The other guys sometimes don't however..

I realise it’s a lot easier said than done, but my initial reaction to this is to say that more training and/or stricter procedures are required.
 
Any chance of being a tad more constructive? Any other tests you would do? Would really help a lot if you could.
 
Last edited:
Any chance of being a tad more constructive? Any other tests you would do? Would really help a lot if you could.

I’m trying to be constructive.
There’s no point adding any more tests if you have people who don’t carry out the full range of tests you currently have.

I don’t know enough about the specific application to suggest a voltage to test at but I’m inclined to suggest an insulation resistance test to identify short circuits.
 
There’s no point adding any more tests if you have people who don’t carry out the full range of tests you currently have.

OP:
And above is the winning statement...

Looks like you need to look at your test procedures and get everyone to follow them before expanding your tests.
 

Reply to Testing station and making it safer? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Hi all, Just looking for some advice, I've been asked to take a look at a brake system on a goods lift. The lift is very old and unreliable with...
Replies
23
Views
4K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock