Discuss This cannot be right! 0.8amp in N and 0amp in L in the UK Electrical Forum area at ElectriciansForums.net

Testing the neutral current on an installation that supposedly has no loads connected isn't a meaningful test as such ie it doesn't prove anything.

Are there any UPS's in the house? Any emergency lights with battery back-up maybe...is there a solar PV installation? If so isolate all of these and retest.
 
Have you tried using the clamp meter on the lighting circuit with the Main switch off- obviously if it's not an rcbo being used as a protective device all of the neutrals will be in the main neutral terminal( along with the supply neutral) which could mean you was picking up a reading from out in the road or thurther down the line
 
Thanks for the helpful suggestions folks. These all seem like possible reasons and nothing to do with insanity. I will proceed to isolate the right circuit tomorrow and do the insulation and polarity/wiring checks . Will let you know the outcome.
 
Are there any UPS's in the house? Any emergency lights with battery back-up maybe...is there a solar PV installation? If so isolate all of these and retest.
Agree - and perhaps have a good look for any signs of foreign supply, as this is a couple of hundred watts (if it's really there) so something is still live.
 
Traced the problem down to both the upstairs and down stairs lighting circuits. When disconnected neutral on these circuits the current meter fell to virtually zero amps.

Measured the resistance between neutral and earth conductors and got approx 6 ohms. If there is a difference in voltage between earth and neutral of say 5volts this will account for the 0.8 amps. It's a TNS supply so I guess it's possible.i forgot to measure it.

Unfortunately I couldn't pin point where the previous problem was because most of the rooms were locked by the occupants.

Thanks for your suggestions folks. This was a real eye opener for changing old fuse boards out in an old house!
 
Traced the problem down to both the upstairs and down stairs lighting circuits. When disconnected neutral on these circuits the current meter fell to virtually zero amps.

Measured the resistance between neutral and earth conductors and got approx 6 ohms. If there is a difference in voltage between earth and neutral of say 5volts this will account for the 0.8 amps. It's a TNS supply so I guess it's possible.i forgot to measure it.

Unfortunately I couldn't pin point where the previous problem was because most of the rooms were locked by the occupants.

Thanks for your suggestions folks. This was a real eye opener for changing old fuse boards out in an old house!
 
Im at a loss as to why you are only clamping the cables to see what current is being draw!

Now you have a neutral to earth fault found that will need sorting prior the the RCD being installed!

A global IR test at the CU would of given you a good indication to where the leakage was or even clamping the tails to see how much leakage was present!!
 

Reply to This cannot be right! 0.8amp in N and 0amp in L in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello wise electricians of the world! I am in the UK. Recently we had a water leak which caused some damage in our home, we are currently trying...
Replies
25
Views
4K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Hi. Have searched the net and the forums first for an answer but had no joy so here goes.. Quick background. My son just bought his first house...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock