Search the forum,

Discuss Time Current Curves of Various MCBs and MCCBs in the UK Electrical Forum area at ElectriciansForums.net

Cookie

-
Reaction score
118
Does anyone have a link to various time current curves relevant to UK MCBs and MCCBs in the 16-1,200 amp range? Specifically, how many times the handle rating does it take for each to trip at 10, 5 and 1 second.
 
As soon as you go beyond 125A kind of area you're usually into specific manufacturers data, although a rough rule of thumb would be the BS / EN series as well.
 
UK MCBs are pretty much standardised with B (3-5 In), C (5-10), and D (10-20) curves in use. However, C and more certainly D, are generally not in domestic use.

EU also has K (sub-set of C/D at 8-12 In) and Z curves (2-3 In, so below B curve)

MCCB are very much a law unto themselves so it is manufacturer specific and frequently device set-up specific as well.

Some MCCB ranges have the "instant" magnetic trip at a fixed point, say 600A and so 16-125A or whatever all have different ratios of continuous-to-instant trip (I think this is more like the USA style of breakers).

Others have fixed (or near-fixed) ratio rather like MCBs over the model's range of In values. As some mid-range MCCB allow the thermal trip to be set over a modest range, you can slightly vary the ratio of continuous-to-instant due to an adjustable 'continuous' setting.

Other high-end MCCB have both a fixed energy-limiting magnetic trip quite high up (say 2kA), and an adjustable near-instant trip done by electronics to allow protection levels to be matched to cable adiabatic limits, selectivity with with down-stream MCBs, etc.
 
Last edited:
This link is for the Hager UK commercial catalogue (13BM download):

Page 98 has the typical MCBs curves, page 130 the "x160" range of MCCB, and page 137 the "x250" MCCB range. Then the tables of cascade/selectivity stuff.

Schneider has a much bigger range of MCCB but as I am not using them I simply don't have the will to try and find the documentation!
 
Nice, thank you for this! :)

Do larger MCBs and MCCBs have similar curves?

4.5 times for 10 seconds, 6 times for 5 seconds and 10-20x for 1 second.
They will be "similar" in the sense the time constants, etc, are engineered to protect typical PVC/XLPE style cable insulation, but not identical. However, I would expect them to be no more than a few times different in terms of time for a given thermal overload ratio.
 

Reply to Time Current Curves of Various MCBs and MCCBs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
619
Hello, I am an American living in Germany. I have some US appliances (120v) that I want to use, so I bought a 5000 Watt step down transformer...
Replies
3
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I have read all I can find about radio 4 and tele switching, but can't find if this changes when our clocks change. It all started when I decided...
Replies
3
Views
316

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock