Discuss Time delay RCD in the UK Electrical Forum area at ElectriciansForums.net

S

sparky87

Hi People,
Carrying out a EIC on a recent cu replacement on a TT system. 100 amp 100MA time delay RCD used up front but cert is asking for time delay in MS- how do i find this out?

Thanks
Adam
 
I know the trip time etc but cert asks for time delay in Ms but doesn't say on any of the rcds I have access too or looked at on line including manufacture data!. I.E 1Ms or 60Ms etc, think I have found that standard S type rcds have a delay of 200 Ms? anybody confirm?
Thanks
 
I know the trip time etc but cert asks for time delay in Ms but doesn't say on any of the rcds I have access too or looked at on line including manufacture data!. I.E 1Ms or 60Ms etc, think I have found that standard S type rcds have a delay of 200 Ms? anybody confirm?
Thanks
Have you tested the RCD?
 
I think you're overthinking this. :)

A BS EN 61008 delay "S" type RCD should trip at x1 I delta N between 130ms and 500ms, as per table 3A in appendix 3 of BS 7671 (as others have said).

So it "holds back from tripping" for anywhere between 130ms and 500ms.

The boxes on the EIC are there to establish that verification has included a comparison of results with relevant criteria.

As you say the next box is "Measured operating time at I delta N" which you have measured at 174ms.

This complies with the specifications of the RCD. Job's a good 'un.

In terms of what number to put in the box: I would put "130-500." A measured time below this would be too short. A measured time above this would be too long.
 
I'm throughly impressed by the talking certificate!

But anyway, why do you need to record the time delay for a non adjustable RCD?

Blindly following what is written on a form without understanding why you are doing it is just plain ridiculous!
 

Reply to Time delay RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
890
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
923
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
Hello, I've been asked to install a supply for a TP air source heat pump to heat a swimming pool. The pool room CU is feed from a barn with a TP...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock