Discuss Time delayed rcd’s and fault protection in the UK Electrical Forum area at ElectriciansForums.net

dlt27

-
Reaction score
26
Have been to a farm today that has a 100mA time delayed RCD main switch covering a DB that has MCB’s on majority of circuits ( less than 32A) and 30mA RCBO’s on sockets, lighting etc.
What I was thinking was does this comply with regs as circuits less than 32A should disconnect in less than 0.2s so because time delayed rcd fitted the circuits just on MCB’s don’t comply.
I thought to comply the RCD must trip within 200mS and before voltage rises above 50v.
Am I correct or am I being daft ( not for the first time )?
 
Is it a tt system,if it is then mcbs may not comply,regarding the install of the cabling.
i would be incline to change mcbs to rcb’os on the mcbs.
The time delay would disconnect in 250 ms,I believe.
 
Last edited:
It is a TT system. Am I right in thinking if I I change time delayed to a normal 100mA then will be ok because it will trip within 0.2s, but if leave as time delayed I would have to fit RCBO’s to everything..
[automerge]1575618235[/automerge]
705.411.1 says just about values of RCD’s, but nothing about time delayed. Thanks
 
What I was thinking was does this comply with regs as circuits less than 32A should disconnect in less than 0.2s so because time delayed rcd fitted the circuits just on MCB’s don’t comply.
Hi - check out BBB Appendix 3 Table 3A for maximum disconnection times. If I’ve understood correctly, you need 200ms and looking at the table some S types will do that.
 
It is a TT system. Am I right in thinking if I I change time delayed to a normal 100mA then will be ok because it will trip within 0.2s, but if leave as time delayed I would have to fit RCBO’s to everything..
[automerge]1575618235[/automerge]
705.411.1 says just about values of RCD’s, but nothing about time delayed. Thanks
If you change the RCD to a non time delayed type, you will find the RCBOs will not achieve selectivity with the RCD, and will cause nuisance tripping of the whole DB.
Bear in mind also that the disconnection time of 0.2 seconds relates to prospective residual fault currents significantly higher than the rated residual operating current of the RCD. Therefore, in line with Wilko's reference to table 3a of appendix 3, it is likely that in the event of a fault to earth, the 0.2 seconds disconnection time will be met.
 
Are you saying at 100mA rcd should trip within 0.2s and anything greater than 100mA will trip quicker than the 0.2s? Thank you
 

Reply to Time delayed rcd’s and fault protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
962
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Hi all Was looking in to the adibatic equasion as our company will not let us add on to a Ring circuit with 1mm cpc.. I want to give some...
Replies
12
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock