Discuss Tncs again Electric gates in the The Welcome Forum area at ElectriciansForums.net

R

Rapid sp4rk

Scenario is

2.5mm swa sent out via 13amp sfs to electric gates from 16amp mcb in consumer unit as part of a tncs/pme earthing arrangement. do the gates really need bonding with 10mm or converting to TT Seems over the top any thoughts on this subject would be happily received
 
Just Ive come across this twice in the last 6 months I agree with you entirely I'm old school an thought this was a strange set up. Not something I would do personally but why would anyone else is my question ?

Gates on last property were max 10m from house at closest point roughly 20m from MET
 
only way to be sure is to test gates as to whether they are extraneous. Megger between gate and MET. if > 22 k Ohms, then no need to bond.
 
And provided it's got 30mA RCD, if the measurement is less than 50V/30mA = 1667 Ohms it's ok too (since a fault to the metal of the gate will cause the RCD to disconnect supply).
 
It's the old tncs outside again Ive personally never bothered to rod a gate post regarding electric gates on a tncs or bonded them with there own dedicated cable generally just earthed using the supply cable usually a 2.5 or 4.0mm earth back to CU was just wondering if anyone else does that Head scratching
 

Reply to Tncs again Electric gates in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
579
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hi Ive looked around and i cant see this particular scenario being discussed. I think i may have been a numpty, but bear with me. I have just...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock