hey guys....

ive downloaded some revision questions for my 2394/95 course i have booked for august and ive come across a question im a little unsure about......even when i have used the regs and GN3 to help. a little help would be greatly appreciated as there is no answer sheet for the questions. Heres the question:

consider the following circuit: A TNS system in a domestic property has a earth fault loop impedance measured at the origin of 0.46ohm. A 4mm2 twin and earth cable with a 1.5mm2 cpc feeds a cooker which is operated by a control unit which has an integral socket outlet. the cooker cable is 35mtrs long and is fed through a 30amp BS3036 fuse in a consumer unit at the origin.

1) state the max disconnection time for the circuit? ( i put 0.4 seconds)
2)state the maximum permissible earth loop impedance if the rule of thumb method is used?

( i used Zs < 0.8 x U/Ia , which gave 230/210 x 0.8 = 0.876ohm)

3)Using the more accurate method state the value of actual earth loop impedance?

(i Used 1/F(Zs +Ze(F-1)) , which gave me 1/1.2x(2.64+0.46(1.2-1) = 2.407ohm)

4) State the approximate disconnection time of this circuit should a fault of negligible impedance occur between phase and earth at the extremity of the circuit when the conductors are at their operating temperature?

(i put "wont trip")

5) state if the disconnection time is acceptable?

(i put "no")

6)what simple change could be made if the circuit does not comply?

(i put "decrease the size of the fuse")

If some is kind enough and has the time, could they check through this for me and if ive gone wrong let me know where.

thank you in advance
 
hey guys....

ive downloaded some revision questions for my 2394/95 course i have booked for august and ive come across a question im a little unsure about......even when i have used the regs and GN3 to help. a little help would be greatly appreciated as there is no answer sheet for the questions. Heres the question:

consider the following circuit: A TNS system in a domestic property has a earth fault loop impedance measured at the origin of 0.46ohm. A 4mm2 twin and earth cable with a 1.5mm2 cpc feeds a cooker which is operated by a control unit which has an integral socket outlet. the cooker cable is 35mtrs long and is fed through a 30amp BS3036 fuse in a consumer unit at the origin.

1) state the max disconnection time for the circuit? ( i put 0.4 seconds)
2)state the maximum permissible earth loop impedance if the rule of thumb method is used?

( i used Zs < 0.8 x U/Ia , which gave 230/210 x 0.8 = 0.876ohm)

3)Using the more accurate method state the value of actual earth loop impedance?

(i Used 1/F(Zs +Ze(F-1)) , which gave me 1/1.2x(2.64+0.46(1.2-1) = 2.407ohm)

4) State the approximate disconnection time of this circuit should a fault of negligible impedance occur between phase and earth at the extremity of the circuit when the conductors are at their operating temperature?

(i put "wont trip")

5) state if the disconnection time is acceptable?

(i put "no")

6)what simple change could be made if the circuit does not comply?

(i put "decrease the size of the fuse")

If some is kind enough and has the time, could they check through this for me and if ive gone wrong let me know where.

thank you in advance

1) state the max disconnection time for the circuit? ( i put 0.4 seconds)
A final circuit less than 32A at a Uo of 230V on a TNS is indeed 0.4s
2)state the maximum permissible earth loop impedance if the rule of thumb method is used?


( i used Zs < 0.8 x U/Ia , which gave 230/210 x 0.8 = 0.876ohm)
Correct
3)Using the more accurate method state the value of actual earth loop impedance?


(i Used 1/F(Zs +Ze(F-1)) , which gave me 1/1.2x(2.64+0.46(1.2-1) = 2.407ohm)
You have used the Zs for the 5 s disconnection time for a BS3036 fuse instead of the Zs for the 0.4 s disconnection time.
Your answer should be fairly close to the value in BS7671 of 1.09 Ω.
I think the question may have been asking for the actual value of the earth loop impedance i.e. what you would expect to measure.
based on Zs = Ze + (R1+R2) however the use of the phrase "using the more accurate method" may mean I am wrong.
4) State the approximate disconnection time of this circuit should a fault of negligible impedance occur between phase and earth at the extremity of the circuit when the conductors are at their operating temperature?

(i put "wont trip")
If you calculate the expected Zs value from the (R1+R2) resistance of the cable at 16.71 mΩ/m and the given Ze.
and then calculate the expected fault current at that point using ohms law I = Uo / Zs and read the disconnection time off the BS3036 graph for that current this should give you the approximate disconnection time.
(the answer It will not trip would be incorrect)


5) state if the disconnection time is acceptable?


(i put "no")
check the answer you got above and see if the time is less than 0.4s.


6)what simple change could be made if the circuit does not comply?


(i put "decrease the size of the fuse")
If you decrease the size of the fuse then you may be subject to unwanted tripping of the circuit as the circuit should have been designed using this fuse as the minimum rating that is greater than the design current (after diversity).
Changing the length of the circuit or the size of the conductors should help but would not be a simple change, but replacing the fuse with a BSEN60898 type B circuit breaker would give you more leeway.
 

Reply to trouble with 2394/2395 revision queston in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
550
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K
I've just started at a new church and the electrics are bit of a shambles. I'm not going to be touching them as I'm not qualified, but one thing I...
Replies
14
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock