Discuss Trying to figure cause of tripping in the UK Electrical Forum area at ElectriciansForums.net

Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,173
Done a CU change today, brief testing before hand I knew there was a problem on one circuit, believed to be the element in the immersion tank so put the very low IR readings down to this.
Fitted new CU with plumber arranged to look at the immersion, changed it and thought that would be that. House previously had no main rcd protection at CU.
When I did the IR testing today before powering up i got >199 on all circuits accept the immersion heater radial.
L-E 0.9 Mohms N-E 3Mohms L-N 2.3Mohms.
So knew something was a miss. Bit of investigation and tucked behind the water tank was a rcd socket with 2 shower pumps plugged in. so the immersion radial does both the tank and a double socket.
Removed rcd socket and got >199 ohms on all tests
Put Rcd socket back in and found that the 2 shower pumps (Both 3 amp fused plug in sorts) would trip the rcd in the consumer unit but not the rcd socket. It had not tripped previously when the old re-wireable fuses were in use. Customer didn't even know it was there!
The pumps when plugged into a normal socket did not trip the CU rcd. The RCD in the Cu would trip with the pumps plugged in but not even working with both showers off.
Ramp tested the rcd socket and it trips at 24mA, The 2 pumps when plugged into a normal socket do not trip the CU rcd, it only trips if plugged into the rcd socket.
Taken it out to achieve discrimination or come 2019 selectivity, but its baffled me as it ramp tests as okay at 24Ma, I put the rcd socket on the upstairs ring and put the vacuum on it, no tripping. so seems as if the 2 pumps are the cause but as said when on a normal 2 gang socket the Cu rcd doesnt trip.
Could it be leakage across both the rcd socket and the 2 pumps combined? Only other thing on consumer unit rcd is the cooker circuit which at 500v IR got >999 on all tests.
its good to know for future reference as I like to know why things tripped.
rcd socket shown below:

20180911_185550.jpg
 
i'd suspect a fault in the RCD socket. with that out of circuit, i understand that nothing trips, even with the loads plugged in.
 
did you use your earth leakage clamp meter?
No as there was a lack of space and it took me enough time trying to even get to and remove the said socket. Did consider it though, but once i got to the tank which at first i believed to be the only load on circuit, it was when i went to disconnect the heater from the radial that i saw the the rcd socket
 
i'd suspect a fault in the RCD socket. with that out of circuit, i understand that nothing trips, even with the loads plugged in.
Thats my thinking but it never tripped before i changed the old plug in fuse board to a modern one, it no longer trips with a normal double socket in and all tests okay, so clearly the rcd socket but not sure what exactly
 
Hi - if you are going back, perhaps test the pumps too ?
I didnt test the pumps themselves, I did plug them into the upstairs ring via an extension lead and they didnt trip the main rcd for the ring. After these were fitted the heating engineer had come and filled the space with pipes making it a damn awkward space to work in, i should get a gold medal for contortionist skills for this job
 
Still not clear what the IR reading was on the pumps though?
Edit as post above crossed over......It'd be useful to eliminate a pump fault
It could be good to know for future reference and peace of mind, I am going back in few weeks to fit some extra sockets, change some plastic accessories for brushed steel so may if time permits have a look at the pumps a bit more.
 
Faulty RCD socket. Not needed now so remove it and replace with normal socket.
You cant test the RCD socket now because of the CU RCD, (unless you bypass) but IMO the socket is stuffed
 
I would say that with the socket in place the house RCD trips, with the socket removed the house RCD does not trip. Ergo the RCD socket is faulty.
Why it is faulty is difficult to say but you could try installing a new RCD socket as a test and see if the house RCD then trips, however with the access limitations this might not be worthwhile (or chargeable to the customer) but since effectively removing the redundant socket solves the problem stick with that.
You could take the socket home and try running things on it and see if it trips your RCD!
 
Sorry, Gavin bit late on your post agree what others have said faulty RCD socket. If you're going back to do further work suggest incorporating new double socket on RFC that is accessible.
 
Those initial IR readings, in the 1-3MΩ range, what was causing those - the pumps, socket or immersion? Clearly even 0.9MΩ isn't going to affect an RCD much with 0.26mA of leakage, but they are low enough to suggest a problem worth finding.
 

Reply to Trying to figure cause of tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock