Discuss TT supply with TNS sub mains in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Would like your opinions on the following setup. 300A 3 phase TT incoming supply feeding 15 units with 50A TNS obviously some link somewhere between Neutral and earth but haven't found it yet. I would think that each unit should be TT not TNS thoughts please
 
Last edited:
Why do you think the units have a TNS supply? Are you sure you have a TT supply and not a TNS supply with the electrode at the intake?
TT or TNS the supply neutral is connected to earth at the substation, its how the installation is connected to that earth which differs.
If the incoming supply is TT then the whole installation must be, you can't then have a DNO supplied earth appear in the middle of the installation?
 
So are the TN-S just distribution circuits? Sounds like all 15 units are relying upon one electrode for earthing.
 
Why do you think the units have a TNS supply? Are you sure you have a TT supply and not a TNS supply with the electrode at the intake?
TT or TNS the supply neutral is connected to earth at the substation, its how the installation is connected to that earth which differs.
If the incoming supply is TT then the whole installation must be, you can't then have a DNO supplied earth appear in the middle of the installation?
I should have pointed out that I am in Africa the whole city is TT it appears that its a common practice to illegally connect neutral and earth in the strangest of places. I have previously found 2.5mm CSA linked between Neutral and earth in a 100A 3 phase DB.
 
This is a UK based forum so it is going to be unlikely we can give you a definitive answer as to whether the set-up contravenes the requirements in place in Africa.
 
That isn't possible. TN-S would would be derived at the origin. A link between a neutral and earth through the installation will not be TN-S or TN-C-S.
What is supplied at the source is TT all units have 5C coming in Ze in the units are between 0.15 and 0.21 Ra at the rod is 3.14 ohms there is a link somewhere turning the TT to TN
 

Reply to TT supply with TNS sub mains in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
477
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
567
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock