bigspark17

-
Arms
Reaction score
718
I have a church with living quarters they used to be two seperate properties. Two dno tn-s supplied into either end of each building.! There is one boiler to do the lot, one water supply one gas supply. The boiler is supplied via one dno but main bonded via the other dno supply.! Any thoughts if there should be main bonding from both dno to where water rnters both properties? Any gaps ive left out ill try fill in!
 
I have a church with living quarters they used to be two seperate properties. Two dno tn-s supplied into either end of each building.! There is one boiler to do the lot, one water supply one gas supply. The boiler is supplied via one dno but main bonded via the other dno supply.! Any thoughts if there should be main bonding from both dno to where water rnters both properties? Any gaps ive left out ill try fill in!
Officially when the property became one, one supply should of been removed. i bet no one informed the DNO. In the past removing surplus supplies were.. whats that word? ohhh free! There might be a contribution cost now. Also electricians cost to marry up the 2 installations assuming 1 supply can take the total load.
 
So it's only the main water and gas supplies and a common boiler that connects the two DNO supplies then. Well the main water/gas supplies will be no different than these services supplying a row of houses. There should be stop cocks provided mind, to enable for the second building to be isolated from the first, ...and main bond accordingly...

The boiler shouldn't need additional bonding, ...it's already bonded via the water and gas pipes, as well as earthed via the boilers electrical supply...
 
Provided that the two supplies are fed from the same incoming location then I would have said that the earthing systems of both supplies should be connected together; since they will already be connected to some extent by the bonding conductors it should be ensured that the two systems are adequately connected together.
If this is done then so long as any earth potentials entering the building are bonded to one supply they will be bonded to the other supply as well.
If the two supplies are not fed from the same incoming supply then there can be problems with potential differences between the two earthing points.
(I think theoretically that the "other" DNO supply would be introducing an earth potential into the property and should be bonded!)
 
It’s unlikely but it is possible for the supplies to be off two separate legs of a distribution network, or even two separate transformers.

What I would suggest is using a wander lead to test for a PD between the DNO earth points.
If there is a difference don’t link them. It only takes a volt or so to set up quite large circulating currents.
 

Reply to two dno supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
829
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
476
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock