One house two immersion tanks either end of the building, house has a good size pv array and battery back up, customer wants iboost on both tanks, now i dont see any problems with this unless both ct clamps would be cancelling each other out? Anyone with any experience of fitting two iboost in one property?
Thanks
 
Not used Iboost but can for-see some serious instability issues. How far are the tanks apart as a single iboost can accommodate 2 X3kw immersions (expected to be in the same tank but cannot see a reason why they could not be different tanks. Basically it prioritises one immersion until it hits its thermostat then switches to the second immersion. The iboost is using pulsed DC to allow it to heat the water at different rates to the maximum of the immersion, hence if its a 3KW immersion but there is only 600W available, it will heat the water just using the 600W, clever but looks a very specific stand alone product.
 
One house two immersion tanks either end of the building, house has a good size pv array and battery back up, customer wants iboost on both tanks, now i dont see any problems with this unless both ct clamps would be cancelling each other out? Anyone with any experience of fitting two iboost in one property?
Thanks
You can only use one per phase.you can run two immersions off one Iboost though
 
You can only use one per phase.you can run two immersions off one Iboost though
The specifications are only 3kW here:

Of course you might be able to use a 4P contactor or a pair of SSR to switch two circuits both simultaneously but you would need to contact the supplier as it might have a fast switching cycle or even do proportional control where a contactor would get trashed.

EDIT: Yes, it does, uses "Pulse width modulation" so you can't use any simple means to double up. Still worth asking about options to do so, or to decouple controllers so they don't fight each other for surplice PV power.
 
You could have a timer that (using a contactor) switches the loads between both cylinders, a cost effective solution as well.
As you know you may need other stuff (like a sperarte supply from a single MCB for both immersers, probably on a seperate DB with the contactor and timer built in the same. You could have a priority set up where one chages up first

Are there cyilnder stats on the water storage?
 
Update its a no go.

Reply from marlec

Thank you for your valued enquiry.

Unfortunately you will not be able to utilise 2 Solar iBoost+ units on the same property. The two units would constantly battle for the excess PV. The unit does have 2 outputs, fro use with dual immersion tanks. However this cannot be used for 2 tanks on opposite sodes of the building as the cable runs cannot exceed 3m.
 
Doesn't surprise me, however, their 3m rule is possibly one to probe at, how far would the cable be to the second tank ?

There are devices out there that can deal with this. I have installed Solar control for a 11KW DHW Cylinder and 2 X Buffer Tank immersions at 6KW each. So i can draw 23KW when the sun is out. I am using a KNX Power Meter to measure the Grid supply which outputs the value to the bus. I then use a number of SR Nor gates and comparators and delays to provide the control of each immersion using a KNX logic module. There is no partial power control of the immersions like Iboost, its just on or off at full power.

Stability whilst Sun is in /out and maintaining battery priority whilst simultaneously maximising the available Solar is the challenge.
 
Update its a no go.

Reply from marlec

Thank you for your valued enquiry.

Unfortunately you will not be able to utilise 2 Solar iBoost+ units on the same property. The two units would constantly battle for the excess PV. The unit does have 2 outputs, fro use with dual immersion tanks. However this cannot be used for 2 tanks on opposite sodes of the building as the cable runs cannot exceed 3m.
 
Update its a no go.

Reply from marlec

Thank you for your valued enquiry.

Unfortunately you will not be able to utilise 2 Solar iBoost+ units on the same property. The two units would constantly battle for the excess PV. The unit does have 2 outputs, fro use with dual immersion tanks. However this cannot be used for 2 tanks on opposite sodes of the building as the cable runs cannot exceed 3m.
8
One house two immersion tanks either end of the building, house has a good size pv array and battery back up, customer wants iboost on both tanks, now i dont see any problems with this unless both ct clamps would be cancelling each other out? Anyone with any experience of fitting two iboost in one property?
Thanks
 

Reply to Two solar iboost in one installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hi, I have a 6kw PV with a 6kw Growatt battery and invertor. I have a solar iboost going to the hotwater tank. Recently I had a Ohme Home Pro...
Replies
2
Views
2K
Just thinking of putting a solar iboost on to a Santon premiere systemfit, as it says there should be " NO electronic controllers between the...
Replies
0
Views
2K
Is it possible for all or at least most electricians to be trained up in the wiring of solar PV installations, particularly the iBoost or Eddy or...
Replies
3
Views
1K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock