Discuss Type A rcd in series or change at the board in the Electric Vehicles Advice Forum area at ElectriciansForums.net
Rcds do not need to be Type A it is that most situations will default you to a Type A.So the EV charger does not have Rcd protection built in which surprises me. Rcd”s need to be A type now.In this case a Rcd that disconnects all live conductors.
It says the following also no rod required..If you are adding to a consumer unit with a spare way and no RCD protection or a split load board with a spare way before the RCD’s (so non-RCD protected) then you can fit an A-Type 30mA RCBO as per the overcurrent protection. recommendations above.How about an EV Charger that already has a type A Rcd built-in. MCB off none rcd side to give you discrimination . Also you will need an EV Tester. What type of earthing arrangement does the property have ? Have you calculated Max Demand ?
Indeed. 722.531.3.101 applies.Rcds do not need to be Type A it is that most situations will default you to a Type A.
Hypervolt normally requires a 2 pole B curve Type A RCD + 32/40A MCB, you can either replace the RCD at the supply to the garage, or supply the garage DB from non RCD side of main DB and fit it in the garage, just don't use 2 RCD's in series.I am to install a car charger that states a type A RVD is to be installed. Can this be put in the garage from the non rcd side of the board or is it better to change the RCD on the board and use that side. I assume it makes no difference
Reply to Type A rcd in series or change at the board in the Electric Vehicles Advice Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.