hi all,

If there is such a thing as 'typical' values, what, in your experience would you consider these to be from equipment such as pc's and other IT, washing machines and any other significant sources?

thanks
 
3mA is at the high end of the range even for a PC, monitor and printer together; it's a sensible allowance for design purposes but I don't think I'ver ever actually registered as high as 3mA from any one consumer electronic product. Typical electronic goods tend to leak 0.1-0.5mA. I have to test some stuff tomorrow so I'll post the specific figures.
 
I believe there is a standard or technical document out there that lists expected values for equipment - it was mentioned in a recent E5 podcast I think, but I forget the name/number of it.

I think it's like most of the other standards - too expensive for most of the people who need it to ever get to see it :rolleyes:
 
Page 26 of the Schneider RCD guide CA908066E has a handy table:
https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=CA908066E+(web).pdf&p_Doc_Ref=CA908066E

It lists a desktop PC at 2mA, printer at 1mA, portable computer (laptop I guess) at 0.5mA where it has a functional earth for EMC control.

It is a generally good guide to read, though obviously pushing their RCDs and telling us that type B is the dog's danglies for the future (not mentioning the price). Also it explains the reasons for "RCD uplift" in Zs measurements with a Fluke MFT on page 60.
 
We used to see some stuff in the 3.5mA region at out work, but they had both inlet EMC filters as part of the IEC socket and also EMC filters in the internal PSUs, hence being about double the typical values seen.
 
And just for fun - there is capacitance between L and E conductors in cables, so there is reactance at 50Hz as well. It’s not much, but I did have a go at measuring the capacitance just now and got 190pF/m (on 4m of 2.5/1.5 with my cheapo multimeter). If I’ve done my maths correctly this will give about 1.4mA leakage current in the CPC for each 100m roll used. Some time back I tried to measure this leakage directly with an earth leakage clamp meter and my best guess from that was about 1mA/100m in the real world.

Next question is - does an RCD even see leakage current with PF=0 ?
 
can some one help me with this problem?
I have one spike guard which has only neutral and line wires. but the sockets on the spike guard are 3 pin, the problem I am facing is that : I am getting current into my earthing line, I have got shocked many times from chargers, fridge surfaces, etc.
I am pretty sure that, there might be problem in the spike guard or in some device?
 

Reply to typical earth leakage values in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
378
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock