Discuss UF cable though block wall in the UK Electrical Forum area at ElectriciansForums.net

cbixel

DIY
Reaction score
0
I am replacing some electrical outlets in the basement of my home. The previous wiring was 12 gauge 2 conductor only, with no ground. I am planning to run 12 gauge 2 conductor with ground. I would think that the best wire to use inside the block wall would be the grey wire that is rated for underground. The wall is an exterior wall.

I am also going to replace the electrical boxes, as many of them are corroded as the walls used to be damp. I have addressed the water issue thoroughly, but still, since it is an exterior wall, would think it best to use the UF cable rated for underground use.

I am not sure which box would be best. I can get the masonry boxes, which seem most appropriate, but they are metal. I can get plastic boxes, which would not be harmed by moisture, but the cable clamping system on these is certainly not as robust as the NM cable clamps that go on the metal boxes.

In an case, code asks for NM cable to be supported within 6 inches of the electrical box, but I am not sure how one would do that if the cable were fished through an existing block wall.

It is quite easy to drop the cable through the block wall, and the holes are already there for the electrical boxes, so I am not really interested in abandoning that for a surface mount system in conduit.
 
I am replacing some electrical outlets in the basement of my home. The previous wiring was 12 gauge 2 conductor only, with no ground. I am planning to run 12 gauge 2 conductor with ground. I would think that the best wire to use inside the block wall would be the grey wire that is rated for underground. The wall is an exterior wall.

I am also going to replace the electrical boxes, as many of them are corroded as the walls used to be damp. I have addressed the water issue thoroughly, but still, since it is an exterior wall, would think it best to use the UF cable rated for underground use.

I am not sure which box would be best. I can get the masonry boxes, which seem most appropriate, but they are metal. I can get plastic boxes, which would not be harmed by moisture, but the cable clamping system on these is certainly not as robust as the NM cable clamps that go on the metal boxes.

In an case, code asks for NM cable to be supported within 6 inches of the electrical box, but I am not sure how one would do that if the cable were fished through an existing block wall.

It is quite easy to drop the cable through the block wall, and the holes are already there for the electrical boxes, so I am not really interested in abandoning that for a surface mount system in conduit.
If you are going to push UF cable through a block wall it has to be sleeved with conduit. I use PVC. Yes every time use plastic boxes and if done right it has a locking tab they will let you push the cable in but not pull it out. Remember at least 1/4 inch of the sheath or jacket has to be in the box. On wire fished through the walls you are not required to staple the wire. Get rid of them metal boxes, they can cause a lot of problems being some people who do electrical work don’t use bushings which can cut the wire
 
I am not quite sure I understand about the PVC. It would seem sensible if I were planning to run cable from the inside of the home to the outside, as you could drill a hole all the way through the block and then line it with PVC pipe. The wire I am running, however, runs from the top of the wall, vertically, down to the outlet, and runs within the block. I am not sure how you would get PVC in there, unless it was the flexible Smurf tube.
 

Reply to UF cable though block wall in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm running a 70ft underground UF cable in 3/4 inch PVC conduit to 2 sheds. The sheds are 3ft from each other. I'm just a DIYer enthusiast so...
Replies
1
Views
763
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
529
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
493
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
796
I am replacing my under counter oven with a new 3kw one, oven is on its own circuit and isolation oven switch, the cable is either 4 or 6mm coming...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock