Sorry I don’t know what the meansIs it a CPC in an appliance flex?
[automerge]1588881346[/automerge]
Where would that beHas it got a CE mark?
[automerge]1588881421[/automerge]
The base of the actual lamp holder seem to be made of plastic or definitely feels like it, but I’m pretty sure the top section is made of metal where the bulb screws inGood, that is correct as long as it is wired the right way round in the lampholder.
The lack of earth (actually correctly called a CPC) would be a concern.
Without examining it difficult to say, but it looks to have insufficient insulation to pass for class II therefore it falls into class I - which requires an earth; I would also like to check it is the correct way round internally, or better still use a compliant lampholder to BSEN60238; check the suitability of the cable; and check the additional insulation to prevent cable damage as it enters, and passes through the internals.
[automerge]1588882028[/automerge]
On the side of the actual lamp holder part this is what it saysGood, that is correct as long as it is wired the right way round in the lampholder.
The lack of earth (actually correctly called a CPC) would be a concern.
Without examining it difficult to say, but it looks to have insufficient insulation to pass for class II therefore it falls into class I - which requires an earth; I would also like to check it is the correct way round internally, or better still use a compliant lampholder to BSEN60238; check the suitability of the cable; and check the additional insulation to prevent cable damage as it enters, and passes through the internals.
250V 250W
E255576 A 28BV
Then a marking that says
PRESS
C UL(R) US
LISTED