Discuss Underfloor heating fault ! Need tracker / tracer not TDR ?? in the Electrical Tools and Products area at ElectriciansForums.net

Soulsurfer

-
Arms
Reaction score
143
As above I need to track down a fault on underfloor heating electric mat or loose cable system as to get a guy to come and find fault area from u.k. is around £2,000 apparently and repair etc.. I'm almost certain that it's going to be a joint on the cold tails but any kit that could be used to locate the area advice wise would be great. Thought TDR but that won't really be the item for a short distance etc.. and only have a good mft, multimeters, oscillators etc.. apparently there is some instrument that pumps 1KV down and a sound sensor that can be used to hear the arcing where the fault is ?
Any ideas appreciated as voltage present but no current draw or continuity. Thanks.
 
Depending on how deep the mat is then a cheap and cheerful tone tracer should work, attach the tone generator to the core and run the tracer along the cable route until the tone cannot be picked up, approximately there is your fault.
However the cheap (£20) ones only trace to about 2-3cm deep.
 
Depending on how deep the mat is then a cheap and cheerful tone tracer should work, attach the tone generator to the core and run the tracer along the cable route until the tone cannot be picked up, approximately there is your fault.
However the cheap (£20) ones only trace to about 2-3cm deep.
Thanks Richard, I have a rather expensive set from teaching fibre installs and copper comms while working for Jersey Telecoms a while back but not sure if will go far enough as this is apparently quite deep into screed. Nexans solid core cables.
 
OK mains power signal tracers/ fuse finders again not very deep but deeper than the battery ones.
otherwise you are on CAT and genny scanning, which seems a little OTT for underfloor heating but cheaper than £2000.
 
OK mains power signal tracers/ fuse finders again not very deep but deeper than the battery ones.
otherwise you are on CAT and genny scanning, which seems a little OTT for underfloor heating but cheaper than £2000.
Ok sound, used to use Cat and Genny on the fibre installs to check u/g cabling routes etc.. for the civils to dig. Apparently this guy from mainland has a tool to locate right down to an area size of a 10p piece but I've never heard of such a thing.
 
Hi bud,have you IR tested the heating wire,at different voltages,to determine the ease of this arcing?
If you generated this arc,at a known frequency,he may be detecting this.
Or you could "clear" this,with some HV shananagins,and have it live,one side...but it's starting to get a bit shady ;)

What makes you suspect the cold tails?
 
Hi bud,have you IR tested the heating wire,at different voltages,to determine the ease of this arcing?
If you generated this arc,at a known frequency,he may be detecting this.
Or you could "clear" this,with some HV shananagins,and have it live,one side...but it's starting to get a bit shady ;)

What makes you suspect the cold tails?
Neighbour had a big flood and another company was called in on the insurance to sort it and apparently neighbour told my friend today that the joint against the wall where black tubing was and jointed with a squeezy tool into like barrel looking connectors fixed his ! I'm guessing it was crimped as spark told him it was badly corroded and breaking there.

I did IR at 250 and 500V and was low. No arcing just apparently a tool / instrument the repair companies have but I can't seem to find much online for sale..
 
There are always ways,and means :)

Not a time or place for trade secrets (not that anyone cares;))

Google up the standard loop tests,messrs Blavier,Varley,Murray and Fisher.

It may give you an idea:)
 
This is an issue,like genital warts. Nobody admits it's a problem,and if you find a way of dealing with it,you keep it to yourself;)

A call to a couple of manufacturers,on repairing their product,will give you an idea of the variation,of the task that dare not speak it's name...

So,NO recommendations,as to a method,due to variety of elements,faults,and liabilities...but...

A HV spark generator,say,off an old diesel hot-washer,can instigate an arc which a small,AM radio antennae can find...i hear.

Prolonged HV arcing,may clear any link,across the fault,which could allow one side only,to carry line voltage,which may be detected,with an adjustable volt-finder...maybe...

The bottom line,as always,is time,and money. In the opposite order.

It can be cheaper,to just plumb in a new radiator :cool:
 
Soulsurfer - this idea is tentative and you would need to co-opt some electronics and computer hobbyists to work up a prototype and do some experiments. Do you have such a club nearby? They may do it for the challenge it presents rather than payment and all you would have to fork out for are some simple components.

Broadly speaking the idea is to listen for an arc at the break in the heating cable - the arc being created and repeated at a rapid rate by a spark generator.

So the first step is to make a spark generator and cobble together a transducer and amplifier and oscilloscope. The transducer needs to be lightly glued to the floor above the heating cable. Is it possible to hear/see the signal on the scope caused by the arc?

Next, take 4 such transducers and make an amplitude monopulse receiver - this enables up/down and left/right with respect to the centre to be indicated by difference and sum signals. see:

monopulse antenna - Google pretraga - https://www.google.co.uk/search?q=monopulse+antenna&tbm=isch&source=iu&pf=m&ictx=1&fir=fkCNCzFqXTSeFM%253A%252CdDJ00sUfmC5c0M%252C_&usg=__kqlIkdJxNgAFndizbKeCK3orhfM%3D&sa=X&ved=0ahUKEwjInPj4r77XAhUIfRoKHch2DK0Q9QEISzAH#imgrc=fkCNCzFqXTSeFM:

What you now need is some sort of visual display like a C scope in radar:

170px-C-scope.png


to display the two difference signals - this is were the computer guys/gals do some work.

If this came together and worked you could locate the sound of the arc - it would of course be when the 4 transducer array has been placed centrally over the point of arcing because then the two difference signals are smallest/zero and the sum signal is largest.

These are the transducers I thought you might try or something similar:

stick on transducers | Rapid Online - https://www.rapidonline.com/catalogue/search?Query=stick%20on%20transducers&Tier=Ultrasonic%20Sensors

This paper helps you understand the frequency range of an spark:

https://www.acoustics-engineering.com/files/SPARK TRAIN MEASUREMENTS.pdf
 
Telectrix prompted me to think again about a simpler scheme.

What about doing what Telectrix said, make a 'decent' spark generator to produce a repeating audibly loud spark and then use a doctor's stethoscope to listen through the floor for the arc/spark? Painstaking, prone work might pay off in localising to an area if not a point. Cheaper, quicker and easier to try out than what I cobbled together in my mind earlier.

Sparker from: car battery, ignition coil, interrupter, HV leads and croc' clips?

or

Gas hob igniter?

We will cause this the TeleMarc method and patent it to become millionaires.
 
Last edited:
What about PCE-CL 20 ? 2 mtrs in soil or walls
50cm in concrete. That should find it no ? £200 for transmitter and receiver unit

I read and watched the short video on the machine. It certainly looks neat and inexpensive. I would call the company or seller because in the technical detail it only says it can find continuous cables/wires or short circuits, See under the highlights tab-

- Locates hidden cables, wires or pipes
- Helps identify short circuits and fuses


whereas your problem is a break in one of the live conductors or a break in/off the heating cable.

You want to find out how the receiver will react as it crosses from one side of the fault to the other.

You also want to know if it has a narrow enough receiving beam not to be confused by signals in the close adjacent parallel lines of the weaved heating element array.

You might want to start a new thread which ask if anyone in the forum has ever used one, specifically to find your or a similar sort of problem.

Please let us know what you find out and how you end up solving this problem.
 
So basically a coil some kind of switch that can handle hv generated like a set of points and croc clip onto the mat tails ?

Yes, an old engine car ignition system with the HV side used to energise the underfloor heating element. I think though that the gas hob igniter is a better ready made sparker;

https://www.wowbbq.co.uk/product/we...MItIjm64PA1wIVCijTCh2CHgcZEAQYASABEgJkAvD_BwE

Stoves Spark Generator - Ignition Unit - https://www.buyspares.co.uk/product.pl?pid=2968966&utm_source=google&utm_medium=base&utm_campaign=products&mkwid=sQg9o1O59&pcrid=166155664440&kword=&match=&plid=&pdv=c&gclid=EAIaIQobChMItIjm64PA1wIVCijTCh2CHgcZEAQYHCABEgJLvvD_BwE

Howden Lamona Hob Ignition Unit / Spark Generator 082638976 - https://www.inter-spares.co.uk/howden/howden-lamona-hob-spare-parts/lam1001/ignition-unit-spark-generator-1-2-3-4.html?gclid=EAIaIQobChMItIjm64PA1wIVCijTCh2CHgcZEAQYHSABEgJ2s_D_BwE

You can also try the off station AM radio to search and listen for under floor spark.

Don't underestimate the power and sensitivity of the ears and brain to locate something - provided you have good hearing in the first place.

You may need a combination or sequence of methods to search and then localise.
 
Last edited:
What you also need to do, whatever search tool you use, is use some form of visual integration and correlation to create a cluster or clusters of detections on the floor surface - you may have more than one fault.

To do this you will need some different coloured sticky dots/labels, and then to co-opt friend and family to each have a go at finding the fault/faults using the various search tools.

After a number of folk have had a go with one or more of the tools, you will either see a random arrangement of dots/labels all over the floor because no tool is any good, or hopefully some clustering where different tools and different people are jointly agreeing on a locality.
 
Have spoken to the chaps at PCE instruments and they think it would definitely work to find the break and can be used dead or live with 240V no problems, I also have two new volt sticks and various other toys to try, spoke also to a woman named Vicky at Underfloor heating services who has guys going out over u.k. fixing faulty ufh but she said any arc device would blow the cables apart ! and only advice from her was take up and fit new mat as it's getting to a point where the faults could keep coming. Thanks all anyway. As far as car style arc etc.. how could you keep the sparks coming ? would it require some kind of automatic repetitive switching magic ? Thanks for all the help.
 
With regard to HV arcs causing damage - it depends on the impedance of the HV sparker. The ones based on a car ignition system or gas hob igniter have an impedance such that they cannot deliver enough energy to cause damage. What I think Telectrix had in mind - 11kV from the local supply company is another kettle of fish! I would use either method on my own ufh electric heating if I had it. The reason being that the domestic mains already has much lower impedance sources of high voltage electricity superimposed on the 230Vac.

If it was me I'd use a gas hob sparker. To use the car ignition coil method, buy a 12 Volt 10Amp Double Pole Double Throw (DPDT) relay - wire the ignition coil in series with one of the the Normally closed contacts and bridge these contacts with a 'condenser'
- Points & Condenser for Lucas 25D 23D 22D 4 & 6 cyl distributor - condensor | eBay - https://www.ebay.co.uk/i/132220164991?chn=ps&dispctrl=1&adgroupid=43106429403&rlsatarget=pla-381255986833&abcId=1128926&adtype=pla&merchantid=7449114&poi=&googleloc=9044962&device=c&campaignid=857233083&crdt=0

Wire the relay coil in series with the 12V supply and the other set of Normally closed contacts.

Do respect the HV output from the ignition coil.

Again, if it was me I'd be employing integration and correlation as I mentioned earlier.
 
Last edited:
Do you have photos of layout , so if you knew a distance from the end it would be any use ?
( are these mats ,a heating element in a conductive tube ?)
..I'm thinking compare capaitances at ends ..
Screen-to-element , If no shorts / dampness leakage
 
Do you have photos of layout , so if you knew a distance from the end it would be any use ?
( are these mats ,a heating element in a conductive tube ?)
..I'm thinking compare capaitances at ends ..
Screen-to-element , If no shorts / dampness leakage
I don't have photos or layout as such as I'm going looking into it for a friend and client in a way but just know its nexan cable solid core type cable not sure if comes as a mat or separately but is apparently fitted into the screed. An only guess / estimate full length of the mat really.
 

Reply to Underfloor heating fault ! Need tracker / tracer not TDR ?? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

R
Been called out to a job where they have recently had underfloor heating installed. Firstly, they have put the sensor close to a central heating...
Replies
4
Views
10K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock