Discuss Understanding wiring for wet underfloor heating? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good replies which has helped me understand heating systems in greater detail. However, I have a more specific question to this particular manifold wiring diagram (see picture).

I understand most of it, but I am unsure how to locate the 'boiler enable' terminals located on the bottom left of the wiring diagram. I'm guessing these must be located in the boiler? (its a combi, no pictures, sorry!) Are they in the boiler, and if so how do I identify them?

Second question... Where it says 'heat enable' in part of the manifold wiring centre, it says LS and LR are volt free. The cable from 'heat enable' to 'boiler enable' is therefore volt free. I initially thought this meant ELV and was just poorly worded. However, I now think it means it can take any voltage from 0 up to 230V, is that correct?

lastly, they supply 2 wiring diagrams. I have attached them both. How do I determine which one to use?

20231120_104942.jpg 20231120_104848.jpg
 
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good replies which has helped me understand heating systems in greater detail. However, I have a more specific question to this particular manifold wiring diagram (see picture).

I understand most of it, but I am unsure how to locate the 'boiler enable' terminals located on the bottom left of the wiring diagram. I'm guessing these must be located in the boiler? (its a combi, no pictures, sorry!) Are they in the boiler, and if so how do I identify them?

Second question... Where it says 'heat enable' in part of the manifold wiring centre, it says LS and LR are volt free. The cable from 'heat enable' to 'boiler enable' is therefore volt free. I initially thought this meant ELV and was just poorly worded. However, I now think it means it can take any voltage from 0 up to 230V, is that correct?

lastly, they supply 2 wiring diagrams. I have attached them both. How do I determine which one to use?

View attachment 112244 View attachment 112245
Hi mate haven't done loads of them but they are simple once you've got the hang of it. Unless you are using their manifold to connect to your entire system which you won't be if your heating cupboard is upstairs you only need a switch live to set it off I can't see the diagram on my phone, someone will point you in the right direction but they are good. If you get any trouble pairing wireless stats ring their technical they are really good as well.
 
I understand most of it, but I am unsure how to locate the 'boiler enable' terminals located on the bottom left of the wiring diagram. I'm guessing these must be located in the boiler? (its a combi, no pictures, sorry!) Are they in the boiler, and if so how do I identify them?
I have UFH8 Heatmiser manifold controllers in our house, but with a Heat Pump system - I'll give my understanding, for what it's worth!
You need the manual for the boiler if the method of external control is not obvious. Boiler manual easy to find on the internet!
Usually at the mains input terminals of the boiler there are L. N, and E, and switched live LS. There may also be links (nearby?) relating to what is going to control the boiler, eg Opentherm, so a link may need to be removed or added. Manual should say what to do when using Ls.
It looks in your case that your controller 'heat enable' terminals need the L from the boiler and then return LS when the controller calls for heat. These volt free contacts are indeed for mains.
lastly, they supply 2 wiring diagrams. I have attached them both. How do I determine which one to use?
The way I see it is that the wiring diagram on the left is the one provided with the thermostat and pertains to fitting that, and the one on the right is provided with the manifold controller, and pertains to that.
Correction - just realised they are consecutive pages from the same manual. I think the first is just illustrating how to connect different thermostats/programmers, whereas the second is for the Neostat thermostat/programmer.
The Neostat Air units I have are individual programmers, and you can set on/off times and temperatures for each individual zone, whereas the more basic thermostats just control temperature.
Hopefully for the things you need to connect they show the same information!
Good luck with the installation.
 
Last edited:
they are simple once you've got the hang of it.
As I posted in a thread a couple of weeks or so ago, the first time I came across one of UFH wiring centres, I took it home, removed the circuit board and traced out the complete circuit diagram. When I could see exactly what did what, it did, as robd wrote, become simple.
It was an hour or two well spent.
 
I think, at a quick glance, you can put the switch live up to your heating cupboard in lr. Assuming your pump is down with your underfloor manifold and the motorised valve is upstairs in the cupboard. Then all you need is L, N and SL at the underfloor. The actuator heads link straight into the manifold you've pictured and link individually to the neo stats.
 
I understand most of it, but I am unsure how to locate the 'boiler enable' terminals located on the bottom left of the wiring diagram. I'm guessing these must be located in the boiler? (its a combi, no pictures, sorry!) Are they in the boiler, and if so how do I identify them?

It depends on the boiler, and where/how you are making the connection.

For example on a larger Worcester boiler the terminal Ls is the live supply out to external controls and terminal Lr is the switched live (live return) to the boiler.
If it is a new boiler these two terminals will have a link between them that you remove in order to connect your controls.

On an older style boiler you wouldn't have a live supply out to external controls, you'd simply have a live and switched live terminal.

Basically check the manual for the boiler in question.

Second question... Where it says 'heat enable' in part of the manifold wiring centre, it says LS and LR are volt free. The cable from 'heat enable' to 'boiler enable' is therefore volt free. I initially thought this meant ELV and was just poorly worded. However, I now think it means it can take any voltage from 0 up to 230V, is that correct?

Volt free is also known as a dry contact or as a relay output.
What it means is that the pair of terminals do not supply a voltage, they are effectively just a switch.
In reality there will be a relay on the PCB with the common and N/O terminals connected to the volt free output terminals.

You connect a permanent live and a switched live to them.

If your underfloor heating is being supplied from the same switched fused spur as the boiler then you simply link the live supply to the UFH controls to the Ls of the volt free output and the Lr becomes your switched live to the boiler.

If your UFH is supplied from a different circuit then the volt free terminals allow you to connect the L and SL of the boiler circuit without creating a dangerous interconnection between the circuits.
 
A combi boiler would normally have permanent LNE and Ls + Lr terminals.
The diagram doesn't show the permanent Live (or Neutral) to the boiler though!.
Both drawings are the same so Ls of PCB connects to Ls in boiler and Lr of PCB connects to Lr on boiler.
 
I really appreciate all the responses so far.
I'm going to the property tomorrow and will have a proper look at the boiler and its controls. I may well come back with another picture!
 
A combi boiler would normally have permanent LNE and Ls + Lr terminals.
The diagram doesn't show the permanent Live (or Neutral) to the boiler though!.
Both drawings are the same so Ls of PCB connects to Ls in boiler and Lr of PCB connects to Lr on boiler.
Thanks for that. I've only dealt with system boilers! Presumably Lsupply and Lreturn.
 

Reply to Understanding wiring for wet underfloor heating? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
701
Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
880
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi. I'm installing a wet underfloor heating system in my own house. What would you recommend as the best smart control system? I can hardwire...
Replies
3
Views
670
What’s the best setup for a system that has a heating system with existing radiators but a wet underfloor heating system is being added to a new...
Replies
3
Views
620

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock