Discuss Understanding wiring for wet underfloor heating? in the UK Electrical Forum area at ElectriciansForums.net

I now have a picture of the boiler wiring. The boiler is a vaillant vuw 306/6-3 (H-GB) ecoFIT pure 830.

The boiler has a L,N,E and RT terminal. The RT terminal stands for room thermostat.

Do I just need the LR in the wiring centre connected to RT in the boiler? This doesn't feel right as I'm completely ignoring the LS in the wiring centre. What exactly is the role of LS and LR? I realise this would also cause the S/L in the thermostat to become live. Both the boiler and wiring centre would be fed from the same FCU. It will also be a lot neater upon completion!

edit.... I've been thinking a bit more.
I think I need (as @Avo Mk8 said) a permanent live (PL) going to LS (this can just be a link in the wiring centre from the PL, or I can take it from the L in the boiler). Then a conductor between LR in the wiring centre and RT in the boiler?

20231215_102334.jpg 20231215_103841.jpg
 
Last edited:
Do I just need the LR in the wiring centre connected to RT in the boiler?

Yes Lr will connect to RT at the boiler, you'll need to connect Ls to a permanent live.
. What exactly is the role of LS and LR?

Ls and Lr are just the normally open contacts of a relay which is energised to call for heat from the boiler or other source of heat.
In your case you need a simple 230V switched live at the boiler so you need only to give Ls a permanent live and connect Lr to the boiler.
If your boiler had a 24V ELV control connection you would connect 24V from the boiler to Ls and the Lr would become your 24V switched live to the boiler.



I realise this would also cause the S/L in the thermostat to become live.

The room stat needs to be disconnected from the boiler switched live terminal otherwise you'll have problems and the whole system will be uncontrollable.

There needs to be a motorised valve installed onto the flow pipe to the existing heating, which it looks like there is from your last picture.
From the wiring diagrams you posted it shows that you can connect the valve and existing thermostat into the heatmiser box.
 
The RT terminal in the boiler is the switch return live.
You should be good linking permanent live to LS in wiring centre or take it from boiler or double up from your fcu. Your choice. If you’re unsure, just remove the plug from the boiler and do all your testing first, before reconnecting it to the boiler. At least if it goes bang, you’re not blowing the boiler pcb.
 
Yes Lr will connect to RT at the boiler, you'll need to connect Ls to a permanent live.


Ls and Lr are just the normally open contacts of a relay which is energised to call for heat from the boiler or other source of heat.
In your case you need a simple 230V switched live at the boiler so you need only to give Ls a permanent live and connect Lr to the boiler.
If your boiler had a 24V ELV control connection you would connect 24V from the boiler to Ls and the Lr would become your 24V switched live to the boiler.





The room stat needs to be disconnected from the boiler switched live terminal otherwise you'll have problems and the whole system will be uncontrollable.

There needs to be a motorised valve installed onto the flow pipe to the existing heating, which it looks like there is from your last picture.
From the wiring diagrams you posted it shows that you can connect the valve and existing thermostat into the heatmiser box.
Many thanks Dave.

With regards your last point, I'd like to understand how it will cause problems. At present the thermostat is purely for the radiators which the plumber is planning to keep as it is, i.e. not being part of the heatmiser box.

If, on the one hand the thermostat calls for heat, this will cause LR to become 230V. I cant see how this is a problem?
If, on the other hand the heatmiser unit calls for heat, I.e. the switch closes between LR and LS, then the S/L terminal of the thermostat becomes live .....

Oh... I think I've just seen your point. Will this now turn the radiators on?
 
But if simply livening up RT causes the radiators to come on, then it will do this anyway even if the conductor from the stat to RT is not there. This means there must be other changes that are required?
 
But if simply livening up RT causes the radiators to come on, then it will do this anyway even if the conductor from the stat to RT is not there. This means there must be other changes that are required?

Yes, as I said above a motorised valve is required on the flow pipe to the radiators which there appears to be already installed in the picture.

If I have understood the photo correctly the pipes with the blue and red lever valves will be the flow and return to the UFH and the, electrically unconnected, motorised valve above the red valve will be in the flow to the radiators.
 

Reply to Understanding wiring for wet underfloor heating? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
702
Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
880
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi. I'm installing a wet underfloor heating system in my own house. What would you recommend as the best smart control system? I can hardwire...
Replies
3
Views
671
What’s the best setup for a system that has a heating system with existing radiators but a wet underfloor heating system is being added to a new...
Replies
3
Views
621

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock