Thanks for that. I've only dealt with system boilers! Presumably Lsupply and Lreturn.
I think that is the logic, but it's not all manufacturers, the labelling of those terminals is arbitrary and could be anything.
Discuss Understanding wiring for wet underfloor heating? in the UK Electrical Forum area at ElectriciansForums.net
Thanks for that. I've only dealt with system boilers! Presumably Lsupply and Lreturn.
Do I just need the LR in the wiring centre connected to RT in the boiler?
. What exactly is the role of LS and LR?
I realise this would also cause the S/L in the thermostat to become live.
You should be good linking permanent live to LS in wiring centre or take it from boiler or double up from your fcu. Your choice. If you’re unsure, just remove the plug from the boiler and do all your testing first, before reconnecting it to the boiler. At least if it goes bang, you’re not blowing the boiler pcb.The RT terminal in the boiler is the switch return live.
Many thanks Dave.Yes Lr will connect to RT at the boiler, you'll need to connect Ls to a permanent live.
Ls and Lr are just the normally open contacts of a relay which is energised to call for heat from the boiler or other source of heat.
In your case you need a simple 230V switched live at the boiler so you need only to give Ls a permanent live and connect Lr to the boiler.
If your boiler had a 24V ELV control connection you would connect 24V from the boiler to Ls and the Lr would become your 24V switched live to the boiler.
The room stat needs to be disconnected from the boiler switched live terminal otherwise you'll have problems and the whole system will be uncontrollable.
There needs to be a motorised valve installed onto the flow pipe to the existing heating, which it looks like there is from your last picture.
From the wiring diagrams you posted it shows that you can connect the valve and existing thermostat into the heatmiser box.
Yes!Oh... I think I've just seen your point. Will this now turn the radiators on?
Oh... I think I've just seen your point. Will this now turn the radiators on?
But if simply livening up RT causes the radiators to come on, then it will do this anyway even if the conductor from the stat to RT is not there. This means there must be other changes that are required?Yes!
But if simply livening up RT causes the radiators to come on, then it will do this anyway even if the conductor from the stat to RT is not there. This means there must be other changes that are required?