I also live in a country where the supply voltage can drop as low as 200v, most refrigerators don't have a problem until around 190-195v when their compressor often fails to start.I run a small ecolodge in rural Laos and have a floating restaurant down on the river with several fridges. Being where we are, the electricity supply is patchy at best. It works nearly all of the time but the voltage rises and falls constantly.
As a result, I invested in a small 3000 VA voltage regulator for the floating restaurant which has two tall upright fridges (bottom part fridge, top part freezer), one ice cream freezer and a small regular fridge plus basics such as lights, a TV, DVD player, amp and toaster. I mainly bought the voltage regulator since the brand new beer fridge I bought wouldn't get cold. The fan and light worked but the compressor wouldn't fire up and I was told that this was because the incoming power to that fridge with everything plugged in hovered between 200 and 210 V which wasn't enough for such a tall fridge and it needed to be a constant 220V.
When acompressor starts you get a very brief large current flowing whilst it starts running then the normal run current will be pretty stable, it will then gradually reduce over a period of several minutes as the evaporating temp comes down (head pressure reduces) and it gets colder inside.I wired the voltage regulator in correctly (although I'm certainly not a qualified electrician it was just simple connections) but it will run perfectly for about ten minutes at 220 V and about 2 amps or even less
It sounds like one of the fridge compressors is stalling. When a compressor stalls it will draw a much larger current (maybe 5 x the run current) for several seconds and possibly up to half a minute until the thermal protection on the compressor disconnects the power automatically. This protector will auto reset in 3-15 minutes usually. This high current would almost certainly cause your 3000VA regulator to trip so all the other fridges would stop. The stalling could be due to several reasons but if the voltage is stable and remains above 210v up to the point of stall then there's most likely a fault on one of the fridges that's causing it.but will then suddenly drop down to about 110-140 V while the amps will shoot up to about 20 amps (Which should trip the 15A breaker on the unit, no?). The lights dim, the fan slows, the fridge compressors stop etc and it will stay like that for a few minutes before you can hear the voltage regulator kick in again and everything will be back to normal. However, this cycle continues constantly.
I'd attempt to run the system with one of the fridges unplugged. If the fault persists then plug that fridge back in and try disconnecting another one. Do this until you figure out which fridge is the rogue one by deduction.
It's also worth noting that if a fridge is restarted quickly after it's been running and has stopped then it will restart or attempt to restart before the gas system has equalised. This load on the compressor, especially domestic fridge compressors will prevent it from starting and again high current draw until the thermal protection causes disconnection. This attempting to rapidly restart may be compounding your problems. It would be a wise move to add some kind of timer to your regulator so if it trips it doesn't reset and reapply power for a period of a few minutes. Similarly it would be advisable to try come up with a system that avoids having all compressors starting simultaneously when power is applied or reapplied because the combination of all the compressor start currents simultaneously would be very high and possibly cause the regulator to trip.
Depends on the total current and the cable length but undersized cables are your worst enemy if you already have low voltage problems.The incoming power to the voltage regulator hovers around 220 V according to my multimeter and the rest of the resort, which is all powered from the same breaker box, doesn't have the same problem
The wire from the main breaker box down to the restaurant is VAF 2 x 2.5 sq. mm 300V. Is that maybe too small?
Definitely not ideal, splash out on a cable at least the same size or larger.Another thought I had was that the small section of wire from the voltage regulator to the restaurant breakers is a bit smaller than the main cable I mentioned before. Could that be a bottleneck? Would something like that cause the situation I mentioned?
Some photos of the general setup, the regulator and the fridges would be helpful if you can attach some to your next reply.