What is the regs on terminating unused cable or even cores of an SWA cable. I know sometimes we can’t remove the cable completely sometimes due to being impractical.
 
Unused cores in a cable which has live conductors in it, or unused singles in trunking/conduit which has live conductors in it, should ideally always be connected to earth. This will prevent capacitively coupled (phantom/ghost voltages) or induced voltages appearing on the conductors.
 
Unused cores in a cable which has live conductors in it, or unused singles in trunking/conduit which has live conductors in it, should ideally always be connected to earth. This will prevent capacitively coupled (phantom/ghost voltages) or induced voltages appearing on the conductors.
Unused cable all together?
[automerge]1591968359[/automerge]
Unused cable all together? So you would ideally Earth all the cores to earth?
 
I'm not aware of any regulation that requires unused cores to be connected to earth.

Most control panels will have multi core cables coming in/going out where not all cores will be used, they are not connected to earth but labelled and terminiated correctly into din rail terminal blocks.
 
I'm not aware of any regulation that requires unused cores to be connected to earth.


Does EAWR regulation 8 cover it ?

Precautions shall be taken, either by earthing or by other suitable means, to prevent danger arising when any conductor (other than a circuit conductor) which may reasonably foreseeably become charged as a result of either the use of a system, or a fault in a system, becomes so charged; and, for the purposes of ensuring compliance with this regulation, a conductor shall be regarded as earthed when it is connected to the general mass of earth by conductors of sufficient strength and current-carrying capability to discharge electrical energy to earth.
 

Reply to Unused SWA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
803
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
414
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
796
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
760
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
477

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock