Discuss Unusual circuit on a EICR in the UK Electrical Forum area at ElectriciansForums.net

Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,173
Been at an apartment doing eicr this afternoon as they want to put it on air BnB, they have gas cooker and hob. owner had kitchen fitted and the fitter it appears used the cooker circuit (10mm T&E, 40 MCB, RCD etc) to feed a single socket, for a built in tall fridge/freezer.
The old cooker switch (recently changed to chrome to match) above the worktop isolates the fridge/freezer
From the cooker connection plate is wired a piece of 2.5mm twin and earth clipped direct behind cupboards into the double socket in the adjacent cupboard which the appliance plugs into.
its not a conventional design by any means, it incorporates an isolation switch (old cooker isolator). all testing comes back as within limits and would disconnect in a fault.
Am thinking a C2? but more i think about it am stuck between C3 or a C2
- 40 amp MCB is over rated for the 2.5mm run of cable to socket.
- enclosure (the cooker plate) not suitable for environment/ installation.
At very least Improvement recommended.

Thoughts?
 
Food for thought.........The regs allow a 2.5mm spur from a ring supplying a double socket where the ccc of the cable is less than the ocpd
 
What is the maximum permissible OCPD rating for a 13A socket outlet?
 
In anycase i will be going back for the remedials. she already said she wanted me to fix anything I found. i do like it when a customer says dont worry about cost! By putting it on Air BnB she reckons she can get over £3k per month for a 2nd floor 2 bed flat in the centre of Bath! 3 times what shed get for a normal tenancy.
I Will change the mcb out for a more suitable rated one, and replace the twin and earth for some heat resistant flex as its behind gas cooker and fit it into a 20 amp flex outlet that will be fitted in lieu of the cooker outlet.
 
Been at an apartment doing eicr this afternoon as they want to put it on air BnB, they have gas cooker and hob. owner had kitchen fitted and the fitter it appears used the cooker circuit (10mm T&E, 40 MCB, RCD etc) to feed a single socket, for a built in tall fridge/freezer.
The old cooker switch (recently changed to chrome to match) above the worktop isolates the fridge/freezer
From the cooker connection plate is wired a piece of 2.5mm twin and earth clipped direct behind cupboards into the double socket in the adjacent cupboard which the appliance plugs into.
its not a conventional design by any means, it incorporates an isolation switch (old cooker isolator). all testing comes back as within limits and would disconnect in a fault.
Am thinking a C2? but more i think about it am stuck between C3 or a C2
- 40 amp MCB is over rated for the 2.5mm run of cable to socket.
- enclosure (the cooker plate) not suitable for environment/ installation.
At very least Improvement recommended.

Thoughts?
Go on air BnB?? tin hat on
 
If the CCC reduction is less than 2 meters no code....
Assuming you're invoking the 3m rule to allow a cable which fails the adiabatic on the fault current, that only applie where both fault protection is omitted (vaporising the cpc probably counts as omission) And, if the cable is unlikely to suffer damage.
T&e in a wall wouldn't comply with the latter, but if it's rcd protected then that could cover the fault protection.
Not sure how the ocpd over 32a would be covered for supplying an accessory though.
I'm not an electrician though!
 
There is no danger to not marking CPCs as green and yellow but that would still be a C3.
Why would it be.
It’s a non compliance which does not give rise to any danger if your talking about the cpc marked green only.
No sleeving then yeah C3 because there is a safety aspect which needs addressing as you are increasing the likelihood of the cpc coming into contact with live parts.
 
Why would it be.
It’s a non compliance which does not give rise to any danger if your talking about the cpc marked green only.
No sleeving then yeah C3 because there is a safety aspect which needs addressing as you are increasing the likelihood of the cpc coming into contact with live parts.

Which is the exact point of a C3. Something that does not give rise to danger but could be improved to meet BS7671.
 
Anybody got any thoughts on my question in #6? What is the maximum permissible MCB rating feeding a 13A BS1363 socket outlet? I would expect the CPC to be OK adiabatically for a B40, but what is the short-circuit rating of the socket and what backup protection is required for things plugged into it? Especially things like wall warts that don't contain a BS1362 HRC fuse.
 
I did investigate this by Googling but found no answer. You can get busbar systems with unfused tap offs in offices with 40 or 50A protective devices.
 
Which is the exact point of a C3. Something that does not give rise to danger but could be improved to meet BS7671.

C3 should be for recommendations for improvement for safety, not purely for the sake of complying with bs7671.

If it was purely recommendations that could improve compliance with BS7671 then all pre-harmonisation cable would automatically be a C3 just for being the wrong colour.
 
Anyone want to enlighten me as to what
"air BnB"is?

Pete999 queried it in previous post and no reply as yet.
as mentioned it is a website that lets you rent out a room or even a whole property for short term rents such as holidays or hen/stag do's. In Bath a flat rented normally would fetch say £1k but as a holiday let that same 2 bed flat can fetch £3k per month upwards. hence why landlords are not renewing tenancies and instead turning to air BnB. the economics outweigh any other consideration. It screw up the local housing market though as it reduces available properties and pushes up other rents.
 

Reply to Unusual circuit on a EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
929
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
681
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
774
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock