Search the forum,

Discuss ***Useful Information For The Working Sparky*** in the Australia area at ElectriciansForums.net

Meter Operatives :eek:

* A minimum of 2 years experience in 3 phase and CT metering exchange works
* Preferably an NVQ or City and Guilds Qualification in a relevant electrical engineering subject
* Operatives must hold a valid certificate of authorisation from the relevant DNO (see note below re DNO accreditation)

* All operatives must hold a valid and current certificate for the following:
- First Aid
- Asbestos Awareness ( training provider )
- CSCS Card

* All operatives must attend a 2 day training course at the --------- Metering training centre – this training will be charged at £ --- per day per operative. At the end of the training, assessments will be carried out and only operatives who demonstrate the necessary level of competence will be authorised and certified to carry out
works on behalf of --------- Metering

* All staff engaged in operational metering activities must have a recently completed enhanced CRB check.
 
Building Regulations ;) do state that structures built of combustible material ( i.e. a wooden shed ) must be at least 2 metres from the main house. ( Useful Junk )

local Building Control. ;)
These rules DO apply to DIY activities, anyone carrying out DIY changes which are notifiable will have to submit a building notice to the local authority before starting work and pay the fee to have the work inspected and tested.

Problems may be encountered when trying to sell a property which has had notifiable electrical work carried out but for which the appropriate certificate cannot be produced.

PAT Test - Extension Leads ;)

Extension Leads
Where extension leads are fitted with a standard 3 pin socket outlet these should be tested as Class1 appliances with the addition of a polarity check. Any such extension leads that are found to be without an earth wire should be marked as defective and removed from service.

The length of an extension lead should be checked to ensure that it is not so great that the appliance performance may be affected by voltage drop. Additionally, the length should not exceed the following:

core area maximum length
1.25mm2 12 metres
1.5mm2 15 metres
2.5mm2 25 metres

2.5mm2 extension leads are too large for standard 13A plugs, although they may be used with BS EN 60309 industrial plugs. Extension leads exceeding the above lengths should be fitted with a 30mA RCD manufactured to BS 7071.

Cable reels must be used within their reeled or unreeled ratings as appropriate.

PAT Test Reasons
1).Faulty electrical appliances and leads are the main cause of accidental fires in commercial buildings, representing over a quarter of all such fires.
2) It is your legal responsibility as an employer to provide a safe working environment
3) The majority of insurance companies now make it a stipulation of your insurance cover.

Portable Appliance Testing ;)
( PAT Testing )
PAT Testing Legislation
The legislation of specific relevance to electrical maintenance is the:

* Health & Safety at Work Act 1974
The Health & Safety at Work Act 1974 is the basis of all Health and Safety Legislation in the UK. The law is all encompassing and sets out the general obligations that:
a. Employers have towards their employees and members of the public and
b .Employers have for themselves, each other and members of the public.
The law requires that an assessment of risk is made and that reasonably practicable measures are put in place to minimise any risk.

It is clear that the law sets out the general guidelines regarding safety.

* Management of Health & Safety at Work Regulations 1999
The Management of Health & Safety at Work Regulations 1999 state:
"Every employer shall make suitable and sufficient assessment of:
(a) the risks to the health and safety of his employees to which they are exposed whilst at work, and
(b) the risks to ensure the health and safety of persons not in his employment arising out of or inconnection with the conduct by him or his undertaking."
Again it is clear that an assessment of risk has to made and reasonably practicable steps taken to minimise such risk.

* Electricity at Work Regulations 1989
The Electricity at Work Regulations 1989 state:
“All systems shall at all times be of such construction as to prevent, so far as reasonably practicable, such danger."
"As may be necessary to prevent danger, all systems shall be maintained so as to prevent, so far as reasonably practicable, such danger."
“ System” means an electrical system in which all the electrical equipment is, or may be, electrically connected to a common source of electrical energy and includes such source and such equipment
“ Electrical Equipment” includes anything used, intended to be used or installed for use, to generate, provide, transmit, transform, rectify, convert, conduct, distribute, control, store, measure or use electrical energy."

It is clear that these regulations require a regime of testing and inspection to maintain portable appliances in a safe condition.

* Provision and Use of Work Equipment Regulations 1998 ( PUWER )
PAT Testing Legislation - The Provision and Use of Work Equipment Regulations (PUWER)
The Provision and Use of Work Equipment Regulations
1998 state:
“Every employer shall ensure that work equipment is so constructed or adapted as to be suitable for which it is provided."
The PUWER 1998 covers most risks that can result from using work equipment. With respect to risks from electricity, compliance with the -Electricity at Work Regulations 1989 is likely to achieve compliance with the PUWER 1998.
- PUWER 1998 only applies to work equipment used by workers at work. This includes all work equipment (fixed, transportable or portable) connected to a source of electrical energy.
- PUWER does not apply to fixed installations in a building. The electrical safety of these installations is dealt with only by the Electricity at Work Regulations

* Workplace (Health, Safety and Welfare) Regulations 1992
Scope of the legislation.
It is clear that the combination of the HSW Act 1974, the PUWER 1998 and the EAW Regulations 1989 apply to all electrical equipment used in, or associated with, places of work. The scope extends from distribution systems down to the smallest piece of electrical equipment. It is clear that there is a requirement to inspect and test all types of electrical equipment in all work situations.

The Electricity at Work regulations states that: ;)
"No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger, or where appropriate, injury, unless he possesses such knowledge or experience, or is under such degree of supervision as may be appropriate having regard to the nature of the work".

The IEE Code of Practice states:
those carrying out the inspection and testing must be competent to undertake the inspection and, where appropriate, testing of electrical equipment and appliances having due regard of their own safety and that of others. What should be considered is that the 'danger' to be prevented, includes not just the dangers which may arise during the testing procedure to the tester and others, but also the dangers which may arise at a later date as a result of using equipment which has not been effectively tested.

The tester must have an understanding of the modes of electrical, mechanical or thermal damage to electrical equipment and appliances and their flexes which may be encountered in any environment.

Training must include the identification of equipment and appliance types to determine the test procedures and frequency of inspection and testing. Persons testing must be familiar with the test instruments used and in particular their limitations and restrictions so as to achieve repeatable results without damaging the equipment or the appliance

PAT Test Equipment Types ;)
There are many European standards and guidance notes regarding portable appliances and equipment, though they do not establish a common and specific definition of such equipment. Even so, there does seem to be a consensus of opinion that such equipment is either hand held whilst being connected to the supply, or is intended to be moved whilst connected to the supply, or is capable of being moved without undue difficulty whilst connected to the supply.

It is usual for this equipment to be connected to the supply via a plug and socket, however this is not a requirement for electrical equipment to be deemed portable or transportable. It is common to define a portable appliance by saying that it is 'anything with a plug top on the end of it'. This is a mistake as it may mean that there are some appliances in the system that are never tested.

The IEE Code of Practice gives guidance on the various equipment types:

Portable appliance
An appliance of less than 18kg in mass that is intended to be moved whilst in operation or an appliance which can easily be moved from one place to another, e.g. vacuum cleaner, toaster, food mixer, etc.
Movable equipment (transportable)
This equipment is either:
18 kg or less in mass and not fixed, e.g. electric fire. or
Equipment with wheels, castors or other means to facilitate movement by the operator as required to perform its intended use, e.g. air conditioning unit

Hand Held equipment or appliances
This is portable equipment intended to be held in the hand during normal use, e.g. hair dryer.

Stationary equipment or appliances
This equipment has a mass exceeding 18kg and is not provided with a carrying handle, e.g. refrigerator

Fixed Equipment/appliances
This equipment or an appliance which is fastened to a support or otherwise secured in a specific location, e.g. bathroom heater

Appliances/equipment for building in
This equipment is intended to be installed in a prepared recess such as a cupboard or similar. In general, equipment for building in does not have exposure on all sides because one or more of the sides, additional protection against electrical shock is provided by the surroundings, e.g. built in electric cooker

Information technology equipment
Information technology equipment includes electrical business equipment such as computers and mains powered telecommunications equipment, and other equipment for general business use, such as mail processing machines, VDU's photo-copiers
 
Last edited by a moderator:
Safe work practices - Managing electrical safety in the workplace ;)
Employers must carry out a risk assessment to identify potential workplace electrical hazards and to access the likelihood of injuries from the exposure to these hazards. This will enable appropriate control measures to be implemented.

General precautions - Always ensure that:
An accessible and clearly identified switch near each fixed machine to cut off power in emergency is provided.
For portable equipment, socket-outlets are close by so that equipment can be easily disconnected in an emergency.
Electrical equipment used in flammable/explosive atmospheres should be designed to stop it from causing ignition.
Double adaptors and 'piggy back plugs' are not used.
The wattage of all bulbs in light fixtures and lamps are checked to make sure they are the correct wattage. Replace bulbs that have a higher wattage than recommended to prevent overheating that could lead to a fire.
Lightbulbs and other equipment which could easily be damaged in use are protected. There is a risk of electric shock if they are broken.
Suspect or faulty equipment is taken out of use, labelled 'DO NOT USE' and kept secure until examined by a competent person.
Where possible, tools and power socket-outlets should be switched off before plugging in or unplugging.
Equipment is switched off and/or unplugged before cleaning or making adjustments.
There is provision for all equipment to be stored carefully, securely and safely.
Workers using electrical equipment are trained and supervised.
Electrical installations are safe eg, by providing enough power outlets.
Worn or frayed cords are replaced.
Leads, wiring and cables are in good condition and in the correct position.
PVC insulation tape should not be used to repair damaged cords. Have the cords replaced.
Machinery is unplugged before cleaning.
Enough socket outlets are providing – overloading socket outlets by using adaptors can cause fires.
All connections to power points are made using the correct plugs.
Isolating transformers and residual current devices (RCD) are used.
The electricity supply is isolated from earth and has a voltage between conductors not exceeding 230 volts.
No part of a crane, digger, excavator, drill rig or other mechanical plant, structure or scaffold is brought closer than 4 metres to an overhead line without the written consent of the powerline owner.
Equipment suitable for the working environment is used, eg, cordless tools for wet and damp conditions.
Electric risks can sometimes be eliminated by using air, hydraulic or hand-powered tools.
The main board is locked and the switches are safe and identified.

Suggested testing intervals for portable RCD's ;)
Testing of non-portable RCDs on switchboards or inbuilt into socket outlets must be carried out on a regular basis. This includes both push button testing by the user and inspection testing for operation by an electrician. Unless operated from time to time, an RCD may "mechanically freeze" and not trip when required.
Push-button testing by the user only confirms satisfactory mechanical performance of the tripping mechanism of the RCD. It does not replace inspection testing for operation by a licensed electrical worker.
As non-portable RCDs are far less susceptible to damage than portable RCDs, they are not subjected to the same testing and inspection procedures.In the case of non-portable RCDs, push button testing is recommended at three monthly intervals.

After tripping out, an RCD must be re-activated only when the cause of the trip has been established and remedial action taken.
( Hire equipment : Push-button test (by user) Before each hire . Test for operation By an Electrician )

:) With some loads it is normal to use a slightly higher rated fuse than the normal operating current. For example on 500 W halogen floodlights it is normal to use a 5 A fuse even though a 3 A would carry the normal operating current. This is because halogen lights draw a significant surge of current at switch on as their cold resistance is far lower than their resistance at operating temperature.

Preliminary Inspection : ;) Pat – Testing ( Disconnection ) Determine whether the equipment can be disconnected from the supply and disconnect if, and only if, permission is received. If permission is not received to disconnect the supply do not proceed with any tests and record that the equipment has not been inspected and label accordingly ←←←

Pat – Testing : ;) Should then be performed and the Code :
Recommends that Three Tests are made; Earth Continuity, Insulation Resistance and Functionality. ←←←
 
Last edited by a moderator:
Can some one explain to me what is meant in this context by "The Origin of the Installation"?

Regs : p/27 ;)
Origin of an installation . The position at which electrical energy is >>> delivered to an electrical installation
 
guy`s please don`t post on here if you would like to show your appreciation please just hit the thank you button, if you have any questions feel free to copy part of ambers post and drop into the relevant section for help. try to keep this thread clear so it`s easier to read for everyone
 
Last edited by a moderator:
Re: PIR reporting and competent persons.

3. Selection and erection in relation to maintainability, including cleaning

Section 529 of BS 7671 deals with the selection and erection of electrical equipment in relation to maintainability of an electrical installation, including cleaning of such equipment, and requires, amongst other things, that provisions are made for the safe and adequate access to all parts of the wiring system which may require maintenance.

All electrical equipment and materials used in an electrical installation should be selected and erected so as to be fit for purpose, suitable for their environment and serviceable throughout the lifetime of the installation.

Regulation 529.2 requires that where any protective measure such as a barrier or enclosure must be removed or opened in order to carry out maintenance, reinstatement of the protective measure should be practicable without reducing the original degree of protection.

Electrical equipment such as isolators, distribution boards, consumer units and other similar enclosures containing controlgear should, wherever practicable, be readily accessible, ideally from floor level (Regulation 513.1 refers).

Luminaires which will require removal for replacing lamps or for cleaning and the like, particularly where fluorescent fittings are involved, should preferably be fitted with a suitable luminaire supporting coupler (LSC) or a suitable plug and socket-outlet arrangement. Such provisions are likely to result in a safer method of working when replacing lamps, and facilitate the cleaning of luminaires by unskilled persons without giving rise to danger. Where luminaires are installed at high level, consideration should be given to providing hoisting facilities so maintenance can be carried out at ground level, or by providing means of access via a suitable mobile elevated working platform (MEWP).

4. Periodic maintenance

Chapter 62 of BS 7671 deals with the requirements for periodic inspection and testing of an electrical installation. Where required, periodic inspection and testing should be carried out to determine whether the installation is in a satisfactory condition and safe for continued use (Regulation 621.1 refers).

It is therefore essential that the wiring system and electrical equipment are so arranged that adequate access to electrical equipment and the wiring system is maintained at all times to facilitate inspection, testing, maintenance and repair (Regulation 132.12 refers).

4.1 Records of maintenance

Records of maintenance, including test results, preferably kept throughout the working life of an electrical installation, will enable the condition of the electrical equipment and maintenance systems to be monitored. Without effective monitoring, duty holders cannot be certain that the requirement for electrical installations to be ‘adequately maintained’ has been complied with (refer item 2).

4.2 Operation and Maintenance (O & M) manuals

Every electrical installation in a place of work should be provided with an Operation and Maintenance (O & M) manual# to enable the user and person responsible for maintenance to discharge their responsibilities under the Health and Safety at Work Act 1974, paragraph 6. Such a manual, for example, may include:

● the installation design specification .
● the as-installed drawings .
● the Electrical Installation Certificate .
● the recommended periodic inspection and test intervals for the installation (including where necessary, different parts of installations) .
● a maintenance schedule for all installed electrical equipment (including the necessary personnel competency requirements) .
● manufacturers technical specifications, including recommended maintenance procedures and intervals .
● safe systems of work and safe isolation procedures .
● all special instructions for the operation and maintenance of equipment, such as access arrangements or powering-down and start-up procedures.

*HSE booklet HSR25 Memorandum of guidance on the Electricity at Work Regulations 1989 does not define the term ‘Duty Holder’ but a duty holder in respect to the EWR is widely accepted as being a person who has overall responsibility for the maintenance, safety and quality of the electrical installation and electrical equipment. In some exceptional circumstances, an employee may be assumed to be the duty holder (HSR25 guidance to regulation 3(2)b refers).

Any person using a mobile elevated working platform (MEWP) must be suitably and adequately trained and authorized to operate it.

# Further information on what should be contained in an O & M manual can be found in BS 4884 Technical Manuals, BS 4899 Guide to user’s requirements for technical manuals and in CIBSE Guide to ownership, operation and maintenance of building services.

PS. Feel free to move it . to the Right Place . ***
 
I'm just bumping some of the older threads in the general electrical forum that had a lot of replies. They might not be current topics, if they're not, just ignore them and they'll soon drop off the list. If you DO wish to add a reply and get the conversation going again, feel free to do so. Your input might help somebody else in the future.
 

Reply to ***Useful Information For The Working Sparky*** in the Australia area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
781
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock