[FONT=&amp]If you are not interested in the LED or lamp indication Biff, but prefer a meter, then why buy a 2-pole voltage tester at all. HSE, GS38 only advises that the use of an approved 2-pole voltage detector for determining the presence or absence of voltage (proving dead) is the preferred method. Therefore there is nothing to stop you doing safe-isolation (proving dead), like any other voltage measurement, with a GS38 compliant MFT on the voltage range, it's just not best practice (ESC, BPG2), and you need to ensure that only a voltage range is selected for safety.
Note:- Approved voltage testers (AVT) that indicate voltage in broad bands do not require calibrating. If the AVT incorporates a meter it requires annual calibration, like any other meter, to assure accuracy.[/FONT]
http://www.hse.gov.uk/pubns/priced/gs38.pdf
http://www.esc.org.uk/fileadmin/user_upload/documents/industry/best_practice/BPG2_09.pdf
 
Last edited by a moderator:
[FONT=&amp]If you are not interested in the LED or lamp indication Biff, but prefer a meter, then why buy a 2-pole voltage tester at all. HSE, GS38 only advises that the use of an approved 2-pole voltage detector for determining the presence or absence of voltage (proving dead) is the preferred method. Therefore there is nothing to stop you doing safe-isolation (proving dead), like any other voltage measurement, with a GS38 compliant MFT on the voltage range, it's just not best practice (ESC, BPG2), and you need to ensure that only a voltage range is selected for safety.
Note:- Approved voltage testers (AVT) that indicate voltage in broad bands do not require calibrating. If the AVT incorporates a meter it requires annual calibration, like any other meter, to assure accuracy.[/FONT]
http://www.hse.gov.uk/pubns/priced/gs38.pdf
http://www.esc.org.uk/fileadmin/user_upload/documents/industry/best_practice/BPG2_09.pdf

I'll get banned for giving that post the reply it deserves.
 
always used to use an apprentice with wet hands, but i ran out of apprentices in 1989.
 
My Fluke T100 will trip RCD's according to the order you test L-N / L-E, you can get them for ÂŁ32 if I shop around.
I briefly owned a Metrel but it got sent back due to parts missing, very poor build quality, Metrels name didn't appear on anywhere, both sides of the casing were a completely different shade and they managed to spell 'safety' wrong on the packaging. I contacted Metrel as I though it was a cheap copy, but they confirmed it was made by them!
 
My Fluke T100 will trip RCD's according to the order you test L-N / L-E, you can get them for ÂŁ32 if I shop around.
I briefly owned a Metrel but it got sent back due to parts missing, very poor build quality, Metrels name didn't appear on anywhere, both sides of the casing were a completely different shade and they managed to spell 'safety' wrong on the packaging. I contacted Metrel as I though it was a cheap copy, but they confirmed it was made by them!

obviously a friday afternoon job.
 

Reply to Voltage / Continuity Testers - feedback required in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi all, Firstly I am new to the forum, so will start by saying hi. I work as an electricians mate, and am joining the forum to gain experience...
Replies
3
Views
675
I will start by apologising to @westward10 as he will have had to take time out to move this thread to the correct section. I am terrible at...
Replies
23
Views
6K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
799
Hi. We have a circuit where some of the sockets have a dangerously high earth loop impedance. This was identified by a professional electrician. I...
Replies
29
Views
4K
My cheap and cheerful voltage tester packed up just before Christmas, so need to replace it (It lasted longer than the more expensive one I had...
Replies
25
Views
4K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock