Search the forum,

Discuss Voltage Optimisation Units in the Electricians' Talk area at ElectriciansForums.net

Andy-1960

-
Esteemed
Arms
Reaction score
575
Hi All,

Have come across a site today where the client has had a voltage optimisation unit fitted on his incoming mains supply.
The supply transformer is rated at 2MVA, and the voltage optimiser at 2250A (which appears to be undersized to me!)
Just wondering if anyone has come across these things and how it may affect the Zs values on the site?
 
Hi All,

Have come across a site today where the client has had a voltage optimisation unit fitted on his incoming mains supply.
The supply transformer is rated at 2MVA, and the voltage optimiser at 2250A (which appears to be undersized to me!)
Just wondering if anyone has come across these things and how it may affect the Zs values on the site?
Hi All,

Have come across a site today where the client has had a voltage optimisation unit fitted on his incoming mains supply.
The supply transformer is rated at 2MVA, and the voltage optimiser at 2250A (which appears to be undersized to me!)
Just wondering if anyone has come across these things and how it may affect the Zs values on the site?
Voltage Stabilizers Yes, optimizer no experience.
 
You might want to consider the effect of voltage imbalance on 3 phase motors. Does the client have a large number of such motors running much of the time? The purpose of the voltage optimiser (regulator/stabiliser would be more descriptive of its purpose perhaps) would be to reduce the percent imbalance. The device is producing these phase voltage outputs 224.1V, 225.6V, 225.8V while supplying phase currents of 1208A, 1183A, 1127A. I think that is pretty impressive.

See: The Basics of Voltage Imbalance - https://www.ecmweb.com/content/basics-voltage-imbalance
 
Last edited:
The improvement in large motors running like that in a factory would be wholly negated by the reduction of the voltage and the extra heat generated by the motors.

There are far better ways of improving motor efficiency and power draw than fitting one of these units.

Not to mention I have yet to see a 400/220V motor. Usually see 400/230.
 
There are far better ways of improving motor efficiency and power draw than fitting one of these units.

I'd be interested to hear a little more about these better (cost-effective) ways. Are you suggesting a device for each motor?
 
VFD control for motors would be better for efficiency.

Then you need to look at cost savings vs initial outlay for the VFDs.

Biggest savings by far are motors used on fans, that control the air flow with dampers. If you only need the fan running at 80% speed, you'll achieve on average a 40% reduction in energy.

If you're clever with their set up, you can also use regenerative functions on slowing the motor down, to back feed into a DC bus used to power other motors. Effectively turning the motors on site into generators. Otherwise slowing a motor down is just wasting energy.

Decent site power factor correction is a must for factory with large motor installs. Although don't go down the route of fitting local power factor correction units to motors. That opens up a whole other can of worms if they are not integrated properly.
 
Rob - thank you.

As you may gather, I think there is more to VO (as I have said ought to be VR/VS and there are some snake oil marketing ploys targeted at the gullible and ignorant which should be taken down ) than first meets the casual eye.

I don't believe in a linear world: I think it is in the reality of inherent non-linearity in machines lies the way some energy savings are made by VO/VR/VS - but that would be too difficult to explain to ordinary business folk hence the snake oil.

So(eg), at 220V rather than 240V it may take 3% say longer to do the same repeated mechanical task (eg move something from a to b) but uses 0.5 % less energy.

Similarly, a store has say 50 fluorescent lights burning 8am to 5pm. What is the cheapest way to dim them? Lower the supply voltage. Do stores get many complaints about dim lighting - I guess not. And the tubes might last say a few months longer.

That repetitive saving and a number of others consequential to having a voltage reduction (dimmer lighting without having to change all the tubes and fittings or fitting swanky remotely controlled lighting) might be worth pocketing - all for the one off fixed cost of fitting a VO ie: a one-off cost effective expenditure. This is why I think the business case satisfies bottom-line businesses in certain situations

I am not saying I am infallibly right on this. But I do think there is economic merit in it in specific cases so it should not be summarily written off. (Yes I get that closed loop thermostatically controlled heaters will use the same energy but to my mind they are linear.)

PS: I do have a VR/VS in my home.
 
And has the unit paid for itself in energy savings yet?
Yes. I also think of all those transformers and motors - the door bell, my wife's air bed, the medical fridge fan, the wifi printer, the bt router, the sky box, two electric reclining chairs...plugged in using less quiescent power.

And not only energy savings - I rarely have to change a halogen lamp, led lamp, cfl lamp and we have around 30 burning each night.
 
Last edited:
Yes. I also think of all those transformers and motors - the door bell, my wife's air bed, the medical fridge fan, the wifi printer, the bt router, the sky box, two electric reclining chairs...plugged in using less quiescent power.

I'm sorry, I just don't see it. Unless you payed pennies for the unit.
 
Voltage Optimisation can make sense on large installations where load balancing reduces copper losses but in domestic or light industrial settings it doesn't help.

It might have had a marginal benefit in the past but now most equipment uses power-conversion ( switchmode supplies) which take as much power as they need. If the voltage goes down the current goes up to compensate, so zero gain or even a slight increase in copper losses.

Filament lamps would have got a bit dimmer when the voltage dropped but LEDs will shine just the same, if they aren't designed to be dimmable. Switchmode supplies make sense for cost and efficiency reasons, but you can't fool them by messing with the mains voltage.

Paradoxically, the way to save power with switchmode supplies is to increase mains voltage, then supply current goes down and the LV wiring losses are reduced, but the differences are minimal and don't justify the cost of an optimiser.
 
So(eg), at 220V rather than 240V it may take 3% say longer to do the same repeated mechanical task ... uses 0.5 % less energy.

Similarly, a store has say 50 fluorescent lights burning 8am to 5pm. What is the cheapest way to dim them? Lower the supply voltage. Do stores get many complaints about dim lighting
.
Just waiting for my local Council to start getting sued , for more pedestrian -vs- car deaths in town , due to poor LED lighting - to save Gov cash to meet cut back targets .... More green to let some
Mother / Father / Student die crossing in same place - now " Un-Seen at night "
(--- Magnum booze , Gets my goat up--)
 
This is my final contribution to this discussion. I looked for some case studies and which businesses had decided to use VO/VR/VS. There are some 'big names' who have 'spent to save'. Unless the case studies have been spun - would the equipment seller or buyer get away with that? - these businesses seem to be able to produce their same outputs for less energy cost. I find it intriguing why that can be and have my own theories which I have hinted at earlier.

Case Studies - GW Energy - http://gwenergy.co.uk/case-studies/

PS: I have no involvement or interests in GWE.
 
Huge savings with VFDs but only if you can reduce the process speed. They don’t save energy if you’re running them at the same DOL speed I believe.

I did some digging into VO when I had my solar fired. Basically snake oil especially in a domestic environment.
 
Last edited:

Reply to Voltage Optimisation Units in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth...
Replies
3
Views
634
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
769
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
320
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock