Discuss Wago connectors in a ring main in the UK Electrical Forum area at ElectriciansForums.net

Bul

-
Reaction score
10
Some Wago connectors are rated at 24 amps and take cable up to 2.5mm. Would you use them on a ring main circuit?
My concern is that if one leg of the ring went open circuit, the wago would be then used on a radial circuit protected by a 32a mcb.

Bul
 
Considering that 2.5mm cable is also rated at 24A (before any correction factors), yes.

Your concern is justified, and that is the reason why I never use ring final circuits, I always wire in radials on 20A breakers.
 
2.5mm cable is rated at 27amps before any correction factors. Nothing wrong with ring finals or 24 amp wagos on a ring, ok if it goes "open circuit" then the circuit has been damaged, the same way a radial circuit might be damaged and loose its cpc.
 
The point is that if the ring circuit becomes a radial circuit the 24 amp rated wago would be on a 32 amp circuit.

and so would the 2.5mm cable. If your talking about altering a ring into a 2.5mm radial then you would have to change MCB to 20amp and 24amp wagos would be ok
 
The point is that if the ring circuit becomes a radial circuit the 24 amp rated wago would be on a 32 amp circuit.

The 2.5mm cable is also rated at 24A. If the ring became a radial, the 24A cable will also only be protected by a 32A breaker. There is no issue with you using the wagos.

Edit: Jonny66 beat me to it :D
 
Great news! Lets all wire our rings on tray and in free air from now on! I quite like the 'industrial look', I reckon it will go well in the living room! I don't think it will take much persuasion to get my customers thinking the same way :D
I know some steam punk type people who would love that look in their houses, cheaper than MICC... :lol:
 
I guess if you could guarantee a very low temp permanently as well (but still within the limits of the cables operating range....) you might just squeeze it up to 32.....
 

Reply to Wago connectors in a ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
Hi, I need to swap out a damaged 30A junction box on an existing ring main circuit and thought I'd replace it with Wago 221 connectors and a Wago...
Replies
3
Views
2K
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
671
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
205

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock