Discuss washer fault issue? in the Electrical Appliances Forum area at ElectriciansForums.net

E

ezzzekiel

customer had recieved a shock from washing machine, had a look today and there was around 50v between washer and sink top.
checked bonding, rcd trip times, circuit zs all came back fine so why the shock? washer appeared quite rusty and corroded around base but rcd never tripped, apartfrom an internal fault on the washer i cant see how the shock occured without disconnection any thoughts anyone?
 
measure resistance between washer casing and coldwater pipe, and from there to MET . could be poor earthing on the machine.
 
Already did mate and it was high, just got me wondering as to why rcd tends to trip out as soon as you look at them but not when they need to
 
leakage current <30mA. if you get that earth fault resistance path down to an acceptable value, then the RCD probably will trip.
 
So washer ( obviously seen better days)
Would need earthing improved to create a better fault path to make it trip so the fault is of insignificant value to cause harm
 
If you're getting a shock from an appliance you're looking for two faults. Firstly theres an insulation fault that's causing a path between the live and the chassis. Secondly there's an earth fault that's allowing the touch voltage of the chassis to rise. Finally the RCD would be a candidate for a thorough testing as well.

There could be a possibility that the sink and tap is at a higher voltage than 0v. This would indicate bonding issues plus a fault causing the leakage (maybe waste disposal motor etc).
 
Is it possible that the PD at the sink is betwen another circuit (not served via the RCD) and the earth bond of the washing machine. I'd check the earth bond of the machine and IR between live+neutral combined and earth (to see if the machine has a fault, or if you're looking elsewhere for an explanation).
 
So poor earth on washer (installation tested) allowing voltage on casing to rise but what's the limiting factor holding it at around 50v
 
So poor earth on washer (installation tested) allowing voltage on casing to rise but what's the limiting factor holding it at around 50v
Not quite. My suspicion is that the 50V PD is higher on the sink (due to a fault elsewhere) and the body of the w/m is at 0V. I think if you PAT test it it'll possibly turn out fine (which would then explain why there's no sign of the rcd tripping ... as it's circuits line/neutral are still in balance).
 
....but what's the limiting factor holding it at around 50v

Input resistance of the testing equipment possibly. You'd probably get a much lower reading with an analogue (or higher reading with a digital if you used an analogue)
 

Reply to washer fault issue? in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
513
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock