Discuss Weird?! Neutral-earth fault in the UK Electrical Forum area at ElectriciansForums.net

Was it ever allowable on previous editions of regs?
I mean, for PV to share RCD with other circuits.
My own house, I had an MCS accredited installer for PV, and its just a breaker tagged onto the end of a split board. And ive seen many a number of customers boards done the same way.... as well as EV charge points just added into DB as well.... where ever there was space.
 
Was it ever allowable on previous editions of regs?
I mean, for PV to share RCD with other circuits.
My own house, I had an MCS accredited installer for PV, and its just a breaker tagged onto the end of a split board. And ive seen many a number of customers boards done the same way.... as well as EV charge points just added into DB as well.... where ever there was space.
Yeah, interested to know the answer to this as well since i thought it was acceptable.
 
No, whilst it has not been specifically prohibited in the past it falls foul of the fundamental principles detailed at the start of the regs book.
Must be thousands of installs like this. No wonder so many company’s jumped on the solar bandwagon and just threw them in.

I’ll get mine changed when I eventually upgrade to an all RCBO board.
 

Reply to Weird?! Neutral-earth fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
387
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock