Search the forum,

Discuss What cable size and breaker would I need for two extractor fans in a public toilet? 1.5mm 3 core and a 20amp rcbo? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

What size cable for 2 extractor fans in a public toilet?
One with a current carrying capacity greater than or equal to the rating of the breaker, with low enough impedance to ensure disconnection times are met and voltage drop is not too high, and greater than or equal to the load, which in turn should be less than or equal to the rating of the breaker.

Of a type suitable for the conditions where installed.
 
One with a current carrying capacity greater than or equal to the rating of the breaker, with low enough impedance to ensure disconnection times are met and voltage drop is not too high, and greater than or equal to the load, which in turn should be less than or equal to the rating of the breaker.

Of a type suitable for the conditions where installed.
Technically correct but somewhat unhelpful
 
What size cable for 2 extractor fans in a public toilet?
Be careful mate. This is a public environment where literally anyone can come into contact with this work, and your neck is on the line as the bloke that installed it.
In the nicest way possible, if you need to ask this you shouldn't put yourself in the firing line.
 
Be careful mate. This is a public environment where literally anyone can come into contact with this work, and your neck is on the line as the bloke that installed it.
In the nicest way possible, if you need to ask this you shouldn't put yourself in the firing line.
Thanks mate, I was just asking as someone’s done it and debating if they had installed the correct cable?
 
Thanks mate, I was just asking as someone’s done it and debating if they had installed the correct cable?
That wasn't very clear from the question!
So you are saying it's currently 20 amp RCBO with 1.5mm 3 core.
Are there any fused isolators for the fans or are they connected directly?
 
At the moment my only answer is that no installation method of 3 core flat PVC 1.5mm cable is rated for 20 amps. I was wondering if there were FCU's by the fans and that overload protection was provided that way.
It's likely the RCBO is oversized but can't be sure without knowing more about the fans who knows.
If the OP has a clamp meter it would be interesting to know the current draw with both fans on.
 
Strictly speaking method C is 19.5 amps. But we won't haggle over 0.5 of an amp. In fact running a 1.5mm directly to the 2 fans is also perfectly safe on a 20amp rcbo. But is it conventional, good practice or advisable? No

Is it not 17.5 amps for a 3 core or am I losing plot again?!

Table 4D2A:

1617917633879.png
 
Last edited:
I was wondering if there were FCU's by the fans and that overload protection was provided that way.
If the rcbo feeds the fans directly than they can be treated like any "End of line" appliance and overload protection omitted. Short circuit protection only required and the 20 amp RCBO covers that
It's likely the RCBO is oversized but can't be sure without knowing more about the fans who knows.
It would be oversized if the 1.5mm was connected to a circuit where the loading can't be controlled directly, like a socket circuit socket
If the OP has a clamp meter it would be interesting to know the current draw with both fans on.
In principle that's not an issue. Both fans won't take more than an amp or 2.Well under the capacity of the cable and the rcbo. The issue is, is the cable going to be protected properly under overload and short circuit conditions. It is Interesting how unconventional situations (like the OP, s) force us to look at a situation that we all know is instinctively wrong but can't immediately explain why (talking about myself here). Then we end up "going back to the drawing board" and having to figure out again.. "Why is this wrong?". Good exercise though!!
 
The issue is, is the cable going to be protected properly under overload and short circuit conditions. It is Interesting how unconventional situations (like the OP, s) force us to look at a situation that we all know is instinctively wrong but can't immediately explain why (talking about myself here). Then we end up "going back to the drawing board" and having to figure out again.. "Why is this wrong?". Good exercise though!!
Thank you for talking that through. I was certainly thinking in terms of overload and fault protection. I get that overload protection could technically be omitted. If (as in the case of many fans) the manufacturer advises 3 amp protection it still doesn't sit right with me that that 60 amps could theoretically flow (B curve) before it shuts off.
Is there a remote possibility of more current being drawn if the if the fan jammed or the windings were damaged and it failed to properly start and just hummed I wonder. Probably unlikely and academic.
 
Is there a remote possibility of more current being drawn if the if the fan jammed or the windings were damaged and it failed to properly start and just hummed I wonder. Probably unlikely and academic.
That's a valid point actually as technically all motors should have overload protection. But the wattage of a standard 4" fan is very low.Should it jam its internal impedence will prevent large currents from flowing and if they did the fan windings would likely burn out long before the supply cable would be troubled. In fact you will sometimes come across fans that have "stuck" and on being released they carry on working. High internal impedence prevents the from burning out
 
Do they make special fans for the UK, different from the millions they make for countries where you can't get any overload protection beyond the circuit OPD?
That is a very good question actually. I think it has less to do with the type of fan and a little more to do with the " fuse culture" in UK (and ROI). The only place (usually) you will find fuses in the continent is at the CU. Of course in UK you are obliged to have 13 amp fused plug tops because of the 32 amp ring circuit. But sometimes you also install fuses for convenience. We may for instance install several FCU, s on a circuit for small appliances whose purpose is to ensure one faulty appliance does, nt take the whole circuit out
 
The reason some manufacturers suggest a 3A fuse is for fire protection so should the fan seize then the theory is the fuse will rupture before the windings overheat and catch fire. There was a study I found online but can't find now where this was put to the test and the success of the 3A fuse was dependent on the manufacturer, some worked whilst some did not.
 
Last edited:
The reason some manufacturers suggest a 3A fuse is for fire protection so should the fan seize then the theory is the fuse will rupture before the windings overheat and catch fire. There was a study I found online but can't find now where this was put to the test and the success of the 3A fuse was dependent on the manufacturer, some worked whilst some did not.
Good comment and new information for me. I must be honest and say I have never installed a 4 " fan that required an inline fuse. I have also not come across them over here (yet). However I must also say I have at times replaced fans without rigidly reading every word in the instruction manuel so that is a good reminder for me
 
The reason some manufacturers suggest a 3A fuse is for fire protection so should the fan seize then the theory is the fuse will rupture before the windings overheat and catch fire.
So are they selling us different fans to the ones they sell in countries where, short of a dedicated circuit, you can't put them on a 3A fuse?
 
OK - so it goes on a 6A, like millions of fans here on lighting circuits.

Are the multinational fan makers producing different products for here, such that our 6A circuits won't do, but French ones will?
 
The requirement for a 3amp inline fuse in the UK is generally from the manufacturer, not a regulation.
Indeed.

So why do they require that in the UK when they don't require it in other countries?

As I said
Do they make special fans for the UK, different from the millions they make for countries where you can't get any overload protection beyond the circuit OPD?

So are they selling us different fans to the ones they sell in countries where, short of a dedicated circuit, you can't put them on a 3A fuse?
 

Reply to What cable size and breaker would I need for two extractor fans in a public toilet? 1.5mm 3 core and a 20amp rcbo? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi , I’m going install a commercial 450mm extractor fan , what size and type of cable should i use ?
Replies
7
Views
471
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
800
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
683
Hello, I currently have two switches in my bathroom. One controls the lights above the sink and the other controls a light above the toilet and...
Replies
0
Views
786
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
550

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock