It's around 1.5HP - if you are using the 260V line the "power" it will consume is around 260 x 5 x 1.73 = 2.25kW (not quite right it's actually VA, but let's keep it simple),
However not all this power is converted to output, so it is normal to take around 60% of this on newer motors and 50-55% on older motors (the "loss" is efficiency and power factor) - giving an output around 1.125kW (then divide by 0.746 to convert to hp) = 1.5HP
Difficulty to actually say as a more efficient motor could give up to 1.8hp output, one less down to 1hp.
This motor could be wired in delta for a 260V voltage, that should be ok for a VFD at 230V from a 230v single phase supply.
Try somewhere like Newton Tesla | Mitsubishi Electric Products, Motors & Gearboxes (newton-tesla.co.uk) if you speak to them they would advise if the motor is suitable.