Discuss What features are a must have on a multifunction tester? in the Electrical Tools and Products area at ElectriciansForums.net

Reaction score
12
Hi all

Im just starting out working part time with an electrician whilst studying for qualifications.

My mentor mentioned that I should keep my eye out for a good second hand tester.

But what features are essential and what are nice to haves?

My mentor mainly works on domestic properties but to complete the NVQ I believe you have to gain experience in commercial and industrial which suits me fine, so I’m after a tester that I can use on the different setups.

I’m in no rush as I’m only just starting out but if I have an idea of what bits I should prioritise I can keep an eye out for the right bit of kit.

Cheers

Nick
 
A multi function tester or MFT, such as the Megger 1552, would be essential. The basic principles of testing apply to all areas of electrical work.
 
If you are going to be doing anything commercial you may need the requirement to test Earth Electrodes, not all MFT's are capable of that test, have a look for something along the lines of the Fluke 1663, but compare to others, most manufactures publish what their MFT's are capable of and compare their models like for like, page 5 for Fluke: https://dam-assets.fluke.com/s3fs-public/166x____umeng0100.pdf
 
Thought a little explanation may be required on the Fluke MFT 1664 auto test sequence.

1/2 test at 0 then 180 no reset required
1 test at 0 trip, reset, then 180 trip, reset
5 test at 0 trip, reset, then 180, trip, don't reset, carry out dead tests, then reset.
 
Hi all

Im just starting out working part time with an electrician whilst studying for qualifications.

My mentor mentioned that I should keep my eye out for a good second hand tester.

But what features are essential and what are nice to haves?

My mentor mainly works on domestic properties but to complete the NVQ I believe you have to gain experience in commercial and industrial which suits me fine, so I’m after a tester that I can use on the different setups.

I’m in no rush as I’m only just starting out but if I have an idea of what bits I should prioritise I can keep an eye out for the right bit of kit.

Cheers

Nick

Get yourself a copy of Guidance Note 3. This covers the testing you will be expected to carry out, describes the equipment you need to perform it and goes into depth about when and how to do it. It is in effect the testing bible as far as BS 7671 goes, so get ahead of the game and start reading it early on... gives you a chance to ask relevant questions, and learn ahead of actually being expected to test for real.
 
Second the above, also get an On site guide, IMO the easiest to understand is from "unite the union" cover says "The Electricians Guide to Inspection and Testing" Based on BS76712018 saying all that the "IET On-site Guide" is a ring bound volume and easier to use as it will not keep closing up on you when referencing anything, unlike the Unite version.
 
Second the above, also get an On site guide, IMO the easiest to understand is from "unite the union" cover says "The Electricians Guide to Inspection and Testing" Based on BS76712018 saying all that the "IET On-site Guide" is a ring bound volume and easier to use as it will not keep closing up on you when referencing anything, unlike the Unite version.

Yes, that's a pet hate of mine - guides printed in such a format that you need an industrial press to keep them open.

The IET version with spiral binding is much better.
 
Another thumbs-up for both the Guidance Notes #3 and the On-site guide. GN3 covers a lot of how & why of testing, and also has some notes on types of test equipment and real-world accuracy to expect, a very useful thing to have read cover-cover at one point for background info.

The OSG is also one of those useful books as it has tables of common circuit limits (e.g. how long you can run XYZ cable on ABC protection, etc) and the Zs limits for testing for common fuses and circuit breakers. It also has handy tables not in the regs for stuff like recommended spacing of cable support clips, etc.

Ideally you want a MFT so only one box to keep an eye on and feed batteries from time to time. That and a volt tester/proving unit would be your basic test kit. Typically you need:
  • Low ohm for earth bonds, R1+R2, etc
  • High ohm at 250V and 500V for insulation testing.
  • AC volts for checking supply in-spec
  • Zs/PFC for supply characteristics and end of circuit check against fuse/MCB values
  • RCD trip times for at least 30mA (final circuit) to 300mA delay (incomer TT, or farm fire protection). You should have at least type AC and type A RCD test available, but type B is needed for some cases now (photovoltaic protection, some EV chargers)
Generally get the best MFT you can afford that ticks the list you need now and maybe in 2-5 years. As already mentioned, auto-RCD is a massive help, you connect up and then just keep resetting the breaker, finally copying the numbers down, or if really fancy saving to PC/laptop/tablet for form-filling.

To begin with I would say you ought to write down values, what you tested, where you did it and any other info like date, etc, in a small note book or diary. Helps sometime!

Other stuff if you look to do commercial work is the earth rod check already mentioned. If you have a supply you can check this using the Zs method, but if installing / commissioning without a safe/dependable supply then you need one that can use earth spikes to measure the rod.

Another MFT feature on some is 3-phase rotation checking and allowing you to measure PFC phase-phase which is handy if end of a long line with delta load and no neutral!
 
Just to add, sometimes a multimeter is handy for checking things but not for proving dead!

Typically they offer AC & DC volts, AC & DC current down to microamps, ohms from typically 1 ohm to 10M (especially in the 100-100k range that MFT don't do well), continuity bleeper, diode check, sometimes frequency and capacitance. Not #1 things for typical electrical work but sometimes for looking at faulty accessories, checking batteries, or working on car electrics, etc.

If looking to get a meter then make sure it is rated to at least CAT III 400V so it won't explode in your face if you make a mistake one day (e.g. measuring amps instead of volts on high current circuit). The safety of electrical test equipment is covered by HSE note GS38 and you will sometimes find that mentioned on spec sheets:

I have a few multimeters myself including an accurate but expensive Fluke 179, but the one that folks on here seem to like best is the Testo 760-1 or its slightly better -2 brother, as the auto-range aspect reduces common mistakes.

Another occasionally handy thing is a clamp ammeter, allows checking AC loads without disconnecting wires and not much risk of burning it out if the load turns out be faulted at kA values. If looking for one for most work, I would get one covering 200A or so max but also going down to mA resolution for checking earth leakage currents. The likes of the HandyMAN TEK775 seems best value, or the (probably identical but better known branded) DiLog DL6518. Of course you can pay up to £500 for fancier or more accurate ones, but my DL6518 has proven OK for the times I needed it.
 
Last edited:

Reply to What features are a must have on a multifunction tester? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

HI, I bought the TIS MFT PRO from CEF, nice touchscreen etc, so in the future I could add on the EV dongle and have a fancy case and tester etc...
Replies
6
Views
2K
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Replies
0
Views
281
Hello,I'm brand new to the forum so sorry if this is in the wrong place. I'm selling my Di-log DL9110 multifunction tester,I've used it no more...
Replies
0
Views
1K
Hello fellow sparks, I’m looking to do my testing and inspection course which starts on the 30th of April, but I have not got much testing...
Replies
0
Views
241
Hi guys I’m at one of the funny times in my career where I can’t decide on what I want to do. I’m wondering if one of you experiences folks can...
Replies
0
Views
181

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock