Discuss What fuse? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
Doing an install - came across a main cut out with the following markings

On the outside - BIGG

Stamped on the inside around the fuse head - LISTING RH80 80A

Any idea what I'm looking at? The house was built late 60s early 70s according to the owner.
 
must have fallen out when he slammed the door.
 
this might help.IET Forums - RHL Type 100 fuse
 
BICC British insulated callander cables is manufacturer and size depends on what is on the barrell inside the cutout fuse
 
It's a BICC RH80 Type 2A fuse carrier, it would of originally contained a BS1361 Type 2A fuse rated =<80A. Without the carrier being removed and the fuse type and rating checked, it's anybody's guess as to what it actually contains (seen fuse wire, 2.5 mm[SUP]2[/SUP] copper wire and steel nails e.t.c. ?)
 
Last edited by a moderator:

Reply to What fuse? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
Replies
13
Views
4K
Doing an inspection and came across this. Feeds are as follows: Cutout to Meter - 25mm Meter to connector blocks - 25mm Connector blocks to...
Replies
64
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock