Discuss what is the green gunky stuff? in the UK Electrical Forum area at ElectriciansForums.net

It's the plasticiser released from degrading PVC compounds such as the cable insulation, which reacts with copper and turns green.
 
Found this some time ago about it.

Green gunge is most prevalent in cables made between 1965 and 1971. The
gunge is degraded di-isoctyl phthalate and is the result of the reaction
between the plasticisor in the insulation and the copper. Between 1965 and
1971 the temprature performance of PVC was uprated by the inclusion of an
anti-oxidant in to the PVC. An unappreciated side effect was that the
anti-oxident encouraged the production of exudate.
Evidence suggests that that high ambient temperatures accelarate the
process. The exudate is of low flammability and low toxicity. Although
unsightly it does not reduce the electrical integity of the conductor or the
insulation.

See also the draft BCA statement (April 2001) below: -

1) PVC
PVC comes in two main grades, plasticised and unplasticised PVC.
Unplasticised PVC (UPVC) is used for example in double glazing window frames
where a rigid material is required.
The PVC used for manufacture of cables is a plasticised PVC that conforms to
the relevant British Standard for the cable type in question.

2) Ageing effects
As a cable ages; (at temperatures above normal ambient), the elongation to
break decreases (also the Insulation Resistance increases). The life
expectancy of a cable is arbitrarily considered to be when the elongation to
break of the PVC is 50%.
A lower elongation to break value could be considered suitable especially
for a fixed wiring cable. Therefore, providing the cable is not subject to
movement or when moved due to inspection of socket outlet or the like, the
PVC does not crack, a much lower value of elongation to break is considered
by some as suitable.

3) Greening
Greening is the appearance of a wet green substance that is a product of an
adverse reaction between certain types of plasticiser and the copper
conductors. This greening, which is a rare occurrence, can happen either
after a long period of time for some cables, or if the cable has been
severely overheated.
The plasticiser itself is a clear oily liquid that is non conductive. The
green substance is a combination of copper oxide and plasticiser which may
become conductive under certain adverse conditions.

4) Action if Greening is found
Therefore whenever this green substance is found at socket outlets etc.
initially it should be removed and the terminations cleaned (gloves should
be used) otherwise it is possible that tracking/overheating may occur. It is
strongly recommended that rewiring should be carried out as soon as
possible.

If further information is required, the original cable manufacturer should
be contacted
 

Reply to what is the green gunky stuff? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been carrying out an EICR on a property and have come across this black tarry substance on 2 of the cables. I have seen the pitch oozing...
Replies
9
Views
4K
I've come to a decision, I just cant do work anymore that involves mad stuff, for example today - 2 bed flat that's had fire damage, someone has...
Replies
4
Views
829
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
212
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
291

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock