Stroma Certification Scheme What RCD for 18th Edition

Discuss What RCD for 18th Edition in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
88
I'm a bit late taking my 18th edition update, I've booked for end of November and have my assessment early December.
I'm gonna do a Consumer unit upgrade for assessment. I've not done one since 18th edition, been a bit quiet.
So I'm looking at RCD's, I typically fit Hager, and their pre-built Consumer units come with two Type 'A'. This covers most domestic scenarios, but when you have a fixed load like ovens with resistive heating element, this should be type 'AC' surly. Assuming most houses will have at least an electric oven, maybe immersion heater and electric shower. I should have thought split boards would have 'A' and 'AC' so you can choose appropriate protection.
Also 17th edition was type 'B', why have we moved away from this?
I know it'll all get covered on the course, but want to get ahead. I would be grateful for any input.
 
In practical terms, the only advantage a type AC rcd has over type A is that it may cost a little less. Although that price difference is almost eliminated now.

You can use type B but they are much more expensive generally, although there's advantages if you have pure dc, but unless you need to support specialist applications, type A would cover most things.

Why would you want to use AC in preference to type A?
 
any body started putting in A rated yet
Considering the IET did not put that for ward and even 18 th been out
and not at the my wholesalers Yet.
the reason I'm asking a chap at the wholesalers screaming I need them now.
 
In practical terms, the only advantage a type AC rcd has over type A is that it may cost a little less. Although that price difference is almost eliminated now.

You can use type B but they are much more expensive generally, although there's advantages if you have pure dc, but unless you need to support specialist applications, type A would cover most things.

Why would you want to use AC in preference to type A?
Actually, having read 531.3.3 (i) & (ii) again properly, I can see 'A' includes everything in 'AC' so in fact, I would not choose 'AC' in preference to 'A'

Thanks for that, I've leant something already.
 
Switching on specific appliances or a combination of electrical loads such as LED lighting can produce electrical transients in the order of several 1000 amps for a very short duration. These transients can cause nuisance tripping of standard non-delay Type AC and A RCDs. To overcome this problem, RCDs including 30mA devices, can be manufactured with transient resistant features- see right hand column in the table. Type AKV, F, B and EV RCDs can withstand a fast transient <3kA/20µs. e.g. the Regulations recommend the use transient resistant RCDs, if the circuit contains surge protection devices (SPDs) on the load side of the RCD.
 
Yes, the SPD is normally on the main bus-bar, though some SPD require a MCB as well.

Generally go with SPD that are OK for 125A or more fuses, as they don't use additional CU slots for any MCB and usually work better (as the MCB has impedance that degrades the SPD effectiveness on short pulses).
 
Would the SPD not be on the supply side in most scenarios?
Yes, as said above, you don't really want a rcd/rcbo upstream of a spd; the spd works by shunting current neutral-earth/cpc and line-earth/cpc so the rcd could operate.

The rcd wouldn't operate quick enough to inhibit the operation of the spd, but would remain tripped after it, so a subsequent surge wouldn't be protected against by the spd as it would be out of circuit.

Most spd are direct on the busbar being protected by the main incoming fuse, or have a dedicated mcb or fuse (unusual these days) within the cu.

Fuses are more common on large industrial sites where the incoming fuses are several hundred amps and three phase.
 

Reply to What RCD for 18th Edition in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Replies
6
Views
796
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Experienced Electrician, C&G 236 Parts 1 & 2, AM 1 & 2 18th Edition Am 2. (JIB Gold Card) I've been out of the trade for some time, but did a...
Replies
2
Views
896
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
615

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock