Hi All

On a job this morning doing an EICR. As you will see from photos main live conductor showing signs of burning out at termination. Checked tightness of termination and main switch all seemed fine. I thought I would check main fuse rating to see rating of this. Supply is tncs with 16mm live conductors and 10mm main earth. On checking main fuse I come across what you can see in photo. A hollow round tube in fuse link terminals. This surely isn't legit? The fuse was sealed so I assume it was supplier that put it in
 

Attachments

  • IMG-20200602-WA0001.jpg
    68.1 KB · Views: 189
  • IMG-20200602-WA0004.jpg
    86.1 KB · Views: 186
  • IMG-20200602-WA0003.jpg
    89.2 KB · Views: 182
  • IMG-20200602-WA0002.jpg
    80.3 KB · Views: 180
One thing that surprised me was no isolator for shower hardwired in. What's your take on that?

What is your take on that? Do you think this is non-compliant with BS7671 and if so do you think it is something which affects safety and therfore needs to be coded?

As a person carrying out EICRs you obviously have a greater than average knowledge of the regulations.
 
My initial reaction is that is wrong, there ought to be an accessible means of isolation, but off-hand I don't know if that is actually required.

Any idea why? Was there an old wall or pull switch that had been bypassed to save upgrading it to match current rating, or simply none ever fitted at all?

No, no signs of any pc. Think it was just initially hardwired without an isolator
 
What is your take on that? Do you think this is non-compliant with BS7671 and if so do you think it is something which affects safety and therfore needs to be coded?

As a person carrying out EICRs you obviously have a greater than average knowledge of the regulations.

My understanding of regs is that there is no actual regulation that specifies need for local isolation? The mcb is adequate to provide the isolation. Although that said shower should be installed to manufacturers instruction but as cannot gain access to this at the most I should note this on report but in terms of a regulation to back up a coding I am not aware of this. I may be wrong and hear others takes on it that is why I ask to be sure.
 
My understanding of regs is that there is no actual regulation that specifies need for local isolation? The mcb is adequate to provide the isolation. Although that said shower should be installed to manufacturers instruction but as cannot gain access to this at the most I should note this on report but in terms of a regulation to back up a coding I am not aware of this. I may be wrong and hear others takes on it that is why I ask to be sure.
Note that not all MCB's are deemed adequate as a means of safe isolation for maintenance and repair, 3871's for example.
 
Agreed but only test and inspect to when installed

No you don't, EICRs are carried out to the current edition of BS7671, as is made plainly clear in BS7671.

It is also made plainly clear that compliance with a previous edition of BS7671 does not necessarily mean that something should be recorded as an observation or altered. A lot of people misread or misunderstand the statement made, it clearly says 'not necessarily' but a lot of people incorrectly read it as 'does not'.
'not necessarily' means that it may or may not be non compliant, but that it cannot be judged as non compliant on the sole grounds of a change having been made to BS7671, it means that the item in question must affect safety or be of provable benefit to the installation to be recorded as an observation.

A good example is the change of conductor colours, red and black conductors do not comply with the current edition of BS7671 but this does not affect safety so there is nothing to report on.
[automerge]1591126904[/automerge]
My understanding of regs is that there is no actual regulation that specifies need for local isolation? The mcb is adequate to provide the isolation. Although that said shower should be installed to manufacturers instruction but as cannot gain access to this at the most I should note this on report but in terms of a regulation to back up a coding I am not aware of this. I may be wrong and hear others takes on it that is why I ask to be sure.

That's my understanding too Regards local Isolators for a shower.

The installation must take account of manufacturers instructions, this was changed from 'must comply with' a few years ago as a lot of manufacturers instructions do not correctly reflect the requirements of bs7671 or were written based on older versions of it.
 
Last edited:

Reply to What the hell is this main fuse? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top