Whats everyones thoughts on this picture ? It was taken in a new build property.
The contractors are still building over the road and the electricians are still working on the building site.
Obviously everyone can see no identification on the switch wires but most of the switches do. What bugs me is the connector block on the CPC, why the hell haven't they taken it to the metal backbox. They have done this on every switch.
I was going to pull them up but every switch has got the little plastic caps over the 3.5mm screws so technically there is no exposed metal.

The only reason I can think they do this is to save time when second fixing, as I guess feeding the switch means multiple CPCs to connect.

Anyone else this this is awful or is it just me.

20180816_131845.jpg
 
It may be within regs but its a bodge, think on the saving on connector blocks, also the wall should have been painted before the face plates had been attached, paint on the face plate nasty paint lines going around the aperture.

How much are these house being sold for as the snagging list will be fun to read.
 
could just be a competition, to see if the sparks could out-bodge the plumbers.
 
Whats everyones thoughts on this picture ? It was taken in a new build property.
The contractors are still building over the road and the electricians are still working on the building site.
Obviously everyone can see no identification on the switch wires but most of the switches do. What bugs me is the connector block on the CPC, why the hell haven't they taken it to the metal backbox. They have done this on every switch.
I was going to pull them up but every switch has got the little plastic caps over the 3.5mm screws so technically
go on you know that you want to get your screwdriver to it. :D
 
Glad everyone is in agreement.
Like i say every switch is like this. Reckon Its done because they have trouble putting 3 or 4 Cpcs into the earth terminal of the KO box, a fly lead would obviously waste valuable time...
Thing is all the time the plastic screw caps are on it compiles even though its dogs mess !

Edit....
I forgot to add, every switch has decorators chaulk round it too.
Walls are just taped, jointed, and painted.
Cheap as chips.
 
Last edited:
Glad everyone is in agreement.
Like i say every switch is like this. Reckon Its done because they have trouble putting 3 or 4 Cpcs into the earth terminal of the KO box, a fly lead would obviously waste valuable time...
Thing is all the time the plastic screw caps are on it compiles even though its dogs mess !

Edit....
I forgot to add, every switch has decorators chaulk round it too.
Walls are just taped, jointed, and painted.
Cheap as chips.
You can get them in, usually 3 as norm 4 with a spur etc etc.

What gets me is that people don't have pride in their work but then again I do understand that if you are not fast enough you can get kicked off site and as the job is nearing completion more corners are cut.
 
How do the plastic caps make it comply, the back box requires earthing regardless.
Im hope your right.
I was told this by an NIC inspector in February (i know, i know) it came up as it was around that time that i noticed click started providing the caps on their accessories.

He agreed that it was not good practice but said the plastic cap provides Insulation, I know the regs state that every point should a earth cable available...

Im happy to bring this up but dont want the bar strewards fobbing me off on a technicality.
 
Glad everyone is in agreement.
Like i say every switch is like this. Reckon Its done because they have trouble putting 3 or 4 Cpcs into the earth terminal of the KO box, a fly lead would obviously waste valuable time...
Thing is all the time the plastic screw caps are on it compiles even though its dogs mess !

Edit....
I forgot to add, every switch has decorators chaulk round it too.
Walls are just taped, jointed, and painted.
Cheap as chips.
There is only 1 cpc, done by someone who shouldn't be doing electrics imo.
 
Range from 210,000- 450,000.
I know you can get a few cpc in the lug.
Its the only logical reason i could think really ;)
thought you paid that much for a dog kennel down south east. even up here jerry-built 4 bed detached ( but only by about 2 ft.) start @ £300k.
 
thought you paid that much for a dog kennel down south east. even up here jerry-built 4 bed detached ( but only by about 2 ft.) start @ £300k.
These are so called affordable housing with some help to buy Part rent part buy jobbies, not particularly big, biggest properties being 4 bed 3 storey.

The contractor is a NICEIC company, think they have around 10-20 so called sparks, you know the kinda outfit... All drink in the same pub every Friday night and arm wrestle each other ;)
 
Just throwing this out there. Maybe that is how that person was taught to do a switch.
I was taught at college to connect the CPC in a connector block if using a plastic pattress.
Could whoever wired the switch in fact be a mate/improver or apprentice and was confused about what to do with the CPC?
Nevertheless probably should be being supervised more closely.
And if it is a qualified electrician then poor show!
 
Just throwing this out there. Maybe that is how that person was taught to do a switch.
I was taught at college to connect the CPC in a connector block if using a plastic pattress.
Could whoever wired the switch in fact be a mate/improver or apprentice and was confused about what to do with the CPC?
Nevertheless probably should be being supervised more closely.
And if it is a qualified electrician then poor show!
Most plastic back boxes have an earth terminal, down right laziness in my book, although perhaps that's how it's taught in the DI courses?
 
You can get separate terminals for dry lining boxes, you normally see the space for them in the corner.
 
Thats rough! Just bang a eyelet crimp on the end and self tap it to the box. Im not overly fussed about the sleeving as if you dont know whats live you shouldn't be playing with it.
 
Thats rough! Just bang a eyelet crimp on the end and self tap it to the box. Im not overly fussed about the sleeving as if you dont know whats live you shouldn't be playing with it.

Why? There’s a perfectly good earth terminal in the box so why would you make an unreliable connection with a self tapper instead?
 
Can only think that the back boxes are all supposed to be plastic, but in some instances metal have been used.
The people doing the installation have been told to make off the CPC into connector blocks.
No one told them what to do if metal boxes have been used.

Probably find all the labour used are mates, improvers or Apprentices.
Probably intended to get a couple of Electricians in to sort it out near the end of the job.
 
Can only think that the back boxes are all supposed to be plastic, but in some instances metal have been used.
The people doing the installation have been told to make off the CPC into connector blocks.
No one told them what to do if metal boxes have been used.

Probably find all the labour used are mates, improvers or Apprentices.
Probably intended to get a couple of Electricians in to sort it out near the end of the job.

That's a good point actually. Majority of new builds I see are plasterboard boxes throughout.
 
Why? There’s a perfectly good earth terminal in the box so why would you make an unreliable connection with a self tapper instead?

Thought it was sheared off, I must be blind. Although a self tapper is a lot more reliable than the soft brass terminals and the cheap back boxes.
 
I would like to see a Regulation whereby the fitting of those caps excludes the requirement for the back box to be earthed.
I agree, and regulation 411.3.1.1 seems to state this.
All i was getting at is do those caps stop the metal backbox from being an exposed conductive part, Im in agreement with you and personally dont think they do. Im sure they are just for decoration.

Theres no doubt its rough ! however if I complain and bring it to the customers attention and it kicks off, I want to be sure. I dont want to come off as being wrong and them wiggling their way ouf of it.
 
The requirement is to earth exposed conductive-parts.
With the little caps, there are no exposed conductive-parts.

I think if you push it, you’ll be told to jog on.
 
Last edited by a moderator:
Just a thought...if a L comes adrift when you take the socket off...that backbox might be live...but if the guys fitting them have only ever encountered plastic, drywall back-boxes, they may not realise the consequences...and if so, they have no place wiring them in, in the first place...in which case, they have clearly had insufficient training.
Mr New House Owner might indeed fit shiny chrome faceplates, and assume the existing chocblock CPC termination was all that was required...
Bloody new-builds...well, you all know I hate 'em!
Plus, it isn't difficult to get 4 CPCs in the earth block thingy, or crimp them...
but then, I am not an electrician, so will put my hard hat on...
 
Just a thought...if a L comes adrift when you take the socket off...that backbox might be live...but if the guys fitting them have only ever encountered plastic, drywall back-boxes, they may not realise the consequences...and if so, they have no place wiring them in, in the first place...in which case, they have clearly had insufficient training.
Mr New House Owner might indeed fit shiny chrome faceplates, and assume the existing chocblock CPC termination was all that was required...
Bloody new-builds...well, you all know I hate 'em!
Plus, it isn't difficult to get 4 CPCs in the earth block thingy, or crimp them...
but then, I am not an electrician, so will put my hard hat on...
There looks like only the one CPC.
 
Won’t be that hard to push when the alternative is paying for someone to go round and check every light switch and make good any damage to the finished decoration.
Or pay a competent person in the first place, mistakes should be rectified.
 
Glad everyone is in agreement.
Like i say every switch is like this. Reckon Its done because they have trouble putting 3 or 4 Cpcs into the earth terminal of the KO box, a fly lead would obviously waste valuable time...
Thing is all the time the plastic screw caps are on it compiles even though its dogs mess !

Edit....
I forgot to add, every switch has decorators chaulk round it too.
Walls are just taped, jointed, and painted.
Cheap as chips.
Part of the problem is that the prices & time scales to do these houses is so tight that every opportunity to cut corners is taken. The caulk round the accessories is probably not the electrical contractors fault. Everybody is on a tight schedule and adopt the attitude "its not my problem".
Regardless, it is a poor job done by the sparky, so no excuse there!

Another thing I like to do on metal back boxes is fold back flat the redundant accessory fixing lugs. I have often found these to have nicked or pinched cables, especially if its a bit busy behind the accessory.
 
also the wall should have been painted before the face plates had been attached, paint on the face plate nasty paint lines going around the aperture.
.

Think you'll find that most developers want the painters & decorators into the building as the last working trade. Stops the grubby hand marks & screwdriver marks from an uncaring electrical bod etc.
 
Im hope your right.
I was told this by an NIC inspector in February (i know, i know) it came up as it was around that time that i noticed click started providing the caps on their accessories.
.

The plastic caps (hate em) are to stop you ---- arsehols taking hours lining up the screw slots on the fixing screws, in a vary OCD type way.
 

Reply to Whats your thoughts on this in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Awful time of a new installation by an idiot! He spent most of his time with his phone attached to his ear held between his shoulder and face...
Replies
50
Views
5K
So how about this metering setup anyone? I have never come across this setup before, and I wonder whether the client would be better off keeping...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top