I know you say 3 phase is iut of your remit but all new supplies from WPD are going to be 3 phase as standard from now on.
Could be a chance grow your skillset.
Assuming there is capacity on the supply (check with dno) even if offered 22kw few cars charge above 7kw on ac anyway
Then fit a few.henley blocks after the isolation switch by the meter and run a small consumer unit for the ev.
Main switch plus mcb will do a 22kw zappi. Can fit 3 ct clamps to monitor the load.
Depending in cable route you may need to factor in rcd protection.