Ok, without wanting to cause too much controversy, when is it acceptable to use method 2 for insulation resistance testing? The term 'when it is unpracticable' is lame IMO and invites lazy testers to forgo a lot of work that would otherwise be necessary. I have, however used it myself!! Would be interested to hear other members interpretations....
 
Can you refresh me on what you mean by method 2 for insulation resistance testing?

Yeah sure...
Connecting live and neutral together and testing IR to earth, therefore foregoing the need to through connect at every light fitting or point on a ring final circuit as mentioned in a previous post today...
 
I thought so, but where is it worded as method 2?

It says in the regs when it is and isn't acceptable...

Furthermore..

On a new installing, it isn't acceptable also.
 
Last edited:
What if you were testing something with a neon on it, eg some kind of appliance wired via FCU?
You'd always do type 2 with portable appliances so why not fixed equipment?
 
I might be reading this post wrong but are you saying that testing Line & Neutral together to CPC should never be done on PIR when its aggreed as a LIM due to say rows and rows of low bay lights etc where you would need a cherry picker or the like to disconnect ???

IMO its in the GN for a reason and when it needs to be used (Test 2) its used but covered on the PIR!!
 
You might use it on a PIR on any installation other than the most basic domestic.The whole idea is to keep dismantling to an absolute minimum to avoid the introduction of faults from fatigued cable cores etc.
 
You might use it on a PIR on any installation other than the most basic domestic.The whole idea is to keep dismantling to an absolute minimum to avoid the introduction of faults from fatigued cable cores etc.

Interesting you say that.... my thoughts were that it was introduced to enable PIR's to be carried out more cost effectively, negating the need to hire in scissor lifts and the like for the loads of high bay light etc, but this whole question of causing more faults by carrying out dead testing during PIR's than actually finding faults is more on the money IMO. In the FM world, theres a lot of talk regards moving to more frequent 'live only testing' and I wonder if this is the way the world is moving.....
 

Reply to When is 'method 2' acceptable?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hello, Not an electrician and I currently live in an apartment building. Over the past few years I have been having abnormal problems with my...
Replies
2
Views
716
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
This question relates to 528.1 of the wiring regs (proximity to electrical services). It states that these bands will be kept separate unless one...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock