Hi, non-electrian here. Just bought a 50's house with old electrics. I expect everything will need replacing eventually, but I can't afford to have it all done at once.

I imagine it's best to start at the supply and work out from there, so I think the priority is a new consumer unit - it's got Bakelite wire fuse holders still!

Trying to engage an electrician to do this job, he says he must do an EICR first, otherwise if he puts a new CU on bad wiring it could 'blow up the whole board'.

Now I'm no sparky but that makes no sense to me. Why would you do all the tests on a system you know is non-compliant? It'd be like taking a car for MOT with flat tyres.

Re. a bad circuit killing the CU - firstly all the circuits currently work, so I can't see how it could be that bad. Secondly, the whole point of RCD+MCB or RCBO is to make the system survive and isolate such faults surely?

Also, I thought EICR was for landlords and tenants, not private owners?

Very much ready to be corrected, I know nothing.IMG_20210903_095011.jpg
 
TL;DR
as a homeowner with a known bad CU, why would I have an EICR done before replacing CU?
Last edited by a moderator:
To use your analogy, you would not know if the flat tyres are caused by bad wheels or an external influence, RCD's and RCBO's are in the main to protect personnel not the installation.

By carrying out an EICR before changing the board any faults present on the system can be corrected prior to the board upgrade.
 
Because the sparks needs to establish that he is putting a new board on a safe and compliant installation. The earthing/bonding needs to be to current regs for example so not as easy as saying starting at the supply and work out from there.
The sparks has to put his name to it so must make sure it is safe and compliant before he signs it off and notifies local authority (Part P Building Regs)
 
EICRs are for any property, not just rentals..

It’s just it’s regulation for landlords to have them done to guarantee safety of their tenants

For the age of the installation, and the possibility of DIY bodge ups in the past, it’s highly recommended, and should be done as part of the board change.

There may be a fault which isn’t serious enough to blow a fuse… that’s if the right size fuse wire is being used…. But it may stop the rcd from staying closed.
 
To use your analogy, you would not know if the flat tyres are caused by bad wheels or an external influence, RCD's and RCBO's are in the main to protect personnel not the installation.

By carrying out an EICR before changing the board any faults present on the system can be corrected prior to the board upgrade.
so I should be worried if they DON'T want to do an EICR?

Also, what's a reasonable cost for this work, including a quality CU with SPD and all RCBOs instead of RCDs+MCBs? It's a 3 bed terraced house in Bristol.
 
Yes.

Go for an all RCBO board, more modern that RCD+MCB's and better protection, been retired for a number of years so I am unable to advise on costs.
 
Hi, non-electrian here. Just bought a 50's house with old electrics. I expect everything will need replacing eventually, but I can't afford to have it all done at once.

I imagine it's best to start at the supply and work out from there, so I think the priority is a new consumer unit - it's got Bakelite wire fuse holders still!

Trying to engage an electrician to do this job, he says he must do an EICR first, otherwise if he puts a new CU on bad wiring it could 'blow up the whole board'.

Now I'm no sparky but that makes no sense to me. Why would you do all the tests on a system you know is non-compliant? It'd be like taking a car for MOT with flat tyres.

Re. a bad circuit killing the CU - firstly all the circuits currently work, so I can't see how it could be that bad. Secondly, the whole point of RCD+MCB or RCBO is to make the system survive and isolate such faults surely?

Also, I thought EICR was for landlords and tenants, not private owners?

Very much ready to be corrected, I know nothing.
To ensure that before the CU is swapped the wiring in the house/dwelling is up to scratch and safe, no good installing an expensive CU on iffy wiring, just throwing good money away, and by the way it is a recommendation only, that an EICR is done before a CU is changed, see the "best practice guide" for swapping a CU it explains it all in there.
 
It would be prudent that someone undertakes some testing for the reasons already mentioned in particular what is the means of earthing and that is just looking at your picture.
 
Looking at the service head that may need a visit from the DNO as it looks like it may be a fused L & N
Almost certainly will have a solid link bar in the neutral even if it was once double fused, though definitely worth checking...

The fabric covered main cables from the meter are probably well overdue replacement too though.

If it is 50s electrics with no upgrades there is also every chance there there is no earth (cpc) on the lighting circuit.

Definitely go with someone who at least does the testing equivalent of an EICR, even if they don't generate the paperwork. Not someone who will just throw the cheapest Consumer Unit on the wall and hope that nothing will trip....
 

Reply to When to have EICR done? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
949
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
906
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
869
Hi all, Does anyone know if I can pay to have an EICR done for part of a house (so I can put plasterboard up etc... safe in the knowledge that...
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top